We have this boiler installed and it's started to give issues.
The service was done and passed ok. But only as there was no noise for the guy to hear.
Radiators are fine.
When hot water is being used it generally seems OK, but sometimes there's a large rumble noise 10-15 secs then it stops.
I haven't been close at this time but have also noticed when showering the boiler setpoint is exceeded. Flame cuts out. Drops temp,and refires. Temp increases, exceeds and flame cuts out.
The expansion vessel is at 1bar so doesn't seem it's that, but other than calling baxi. What can I check next?
Video to show the temp fluctuations available.


Thankw
 
Could be the PHEX (plate heat exchanger) is fouled, it may run OK at low HW demand but trip out on high demand.
"have also noticed when showering the boiler setpoint is exceeded" Is this the DHW setpoint thats exceeded by the actual DHW temperature?. If so could be different problem. Can you run two HW taps at full (HW) flow and see if the same problem occurs.
 
No video attached, also how old is the boiler? Could be plate hex as above, but can be other things too.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Potterton promax 40erp HW issue" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

Joined
Location
Leicester
Member Type
DIY or Homeowner

Thread Information

Title
Potterton promax 40erp HW issue
Prefix
N/A
Forum
Central Heating Forum
Start date
Last reply date
Replies
3

Thread Tags

Tags Tags
potterton

Thread statistics

Created
mrpled,
Last reply from
Knappers,
Replies
3
Views
777

Weekly or Monthly Email Digest

Back
Top