Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Scott_D

Esteemed
Plumber
Gas Engineer
Subscribed
Nov 20, 2012
6,128
2,736
113
BRISTOL
Been to look at two boiler changes this week. Got to send off the quotes on the weekend.
At both the boiler is to go upstairs at the back of the house, one has a full width ground floor extension the other a full width conservatory with perspex/plastic roof.
Can the PRV be terminated back to the wall above these roofs?
 
If its turned back against the wall and theres a fair drop to the conservertory, i dont see a problem.

Now wait for the shouty brigade, quoting bs numbers and what not
 
  • Like
Reactions: 2 people
If its turned back against the wall and theres a fair drop to the conservertory, i dont see a problem.

Now wait for the shouty brigade, quoting bs numbers and what not

use a nice little mushroom to look neat and tidy and water is all cool before it reaches any roofing
 
  • Like
Reactions: 2 people
As long as the PRV is terminating safely ie. turned to wall there is absolutely no problem with this.
 
to be honest the only time you really see a prv doing much more than a dribble is when the filling loops been left o and then its cold anyway
 
Thanks chaps
Would be interested to know if there is a BS or reg its against.

From current BS 6798:2009

Specification for installation and maintenance of gas-fired boilers of rated input not exceeding 70 kW net

5.4.3 Pressure relief valve
...
5.4.3.2 The location and method of fitting the pressure relief valve shall be such that:
a) the discharge pipe for water or steam from the valve is metallic and falls throughout its length; and
b) the discharge is visible and will not discharge on to the occupants of the premises or on to any electrical components or wiring.

COMMENTARY AND RECOMMENDATIONS ON 5.4.3
In addition to the requirements of 5.4.3.2 the pressure relief valve should be located where its discharge is unlikely to cause damage to the premises.
It is essential that the pressure relief valve will not stick in the closed position and that it will reseal.
A pressure relief valve is not necessary for an open system.


As soon as the discharge hits the wall, the discharge temperature will fall and it shouldn’t damage the roof. I’d say you are good to go.
 
  • Like
Reactions: 2 people