Hey guys long time since I have posted here but know some of you know your salt. I've got a job in a townhouse and currently the boiler sits on the second floor of a three story but I'm moving it to the ground floor as per client request, problem is, its got ridiculously high ceilings, I'm going to double check but suspect at the very least top floor rads are 7 meters up.. so I'm concerned about a standard 15/60 or whatever being man enough, I've been looking at the 25/80 as a viable alternative but I'll be honest I really don't have a great deal of experience in pump sizing, I'm usually just whacking in combis and forgetting about it 🥴 so I keep hearing that it'll make the system noisy and all these horror stories, just wondering if anyone could give me some advice basically. Current system is 22mm flow + return, currently open vented, 10 rads overall, I'm going to seal it and putting in a 180l unvented indirect. Also, client is a bit of an eco warrior so they want me to put in electric, electric boiler needs 12lpm minimum according to Mi's. Cheers
 
As it’s sealed and the return will equal out the flow so your pump won’t have to work as hard

with open vent it will hep but not as much
I see, so in theory the weight of the water coming back down the return contributes to the force of propelling it up. At what point would it be worth uprating the pump given this effect?
 
Madness I've done several electric systems and they ain't cheap to run you need economy 18 and a super insulated property I certainly wouldn't advise fitting one if there is gas available you will treble their energy bill , pump wise ? dab are my go to pumps as below . Regards kop
 

Attachments

  • Screenshot_20210705-201621.png
    Screenshot_20210705-201621.png
    492.4 KB · Views: 49
  • Screenshot_20210705-201718.png
    Screenshot_20210705-201718.png
    339.2 KB · Views: 45
  • Screenshot_20210705-201658.png
    Screenshot_20210705-201658.png
    487.4 KB · Views: 55
  • Screenshot_20210705-201635.png
    Screenshot_20210705-201635.png
    351.1 KB · Views: 50
Madness I've done several electric systems and they ain't cheap to run you need economy 18 and a super insulated property I certainly wouldn't advise fitting one if there is gas available you will treble their energy bill , pump wise ? dab are my go to pumps as below . Regards kop
it is madness, I turned the job down initially saying to get some quotes locally for a combi install, its cheaper etc but they came back and said "no, we want electric" I said okay, and here I am. Thanks for the recommendation you think ill need the 8m head? I tried dab pumps once, I don't really like the electrical connector block inside the cheaper range, I had a faulty one from new mileeees away once. Very annoying.
 
This may have already been said but the height of a building has no bearing on the pump size required. The system is already filled and the pumps are circulatory, not lifters. As long as the pump can supply the pressure for the flow rate required to overcome the index circuit and heat exchanger resistance then you're ok. Again height is nothing to do with it.
 
  • Like
  • Informative
Reactions: Timmy D and Chester
This may have already been said but the height of a building has no bearing on the pump size required. The system is already filled and the pumps are circulatory, not lifters. As long as the pump can supply the pressure for the flow rate required to overcome the index circuit and heat exchanger resistance then you're ok. Again height is nothing to do with it.
thanks for clearing that up, i wonder when i see insta photos of 2 magna 1's and a llh on a 5 bed house whether its overkill, now im starting to think yes, yes it is... that poor customers wallet.
 