D

Desi80

I've got a rad that was leaking a decent amount of water, tried nipping things up but it didn't help. Yesterday I thought I'd quickly whip the nut off and repack the gland spindle and add a bit of PTFE when reattaching the nut.
I undid the top nut but there' s a black plastic/rubber inner that's risen up and it's stopping me reattaching the top nut. (see attachment)


So now I'm guessing it's time to replace the valve, there's another one I can do whilst I'm at it too.
I've got a pressurised combi system. My checklist is as follows:


• Make sure water feed and power to system is off
The water feed is the valve in the airing cupboard I use to top up pressure right?
• Drain system with a hose and jubilee clip, the drainage point is on the rad in question
• Replace valves
• Refill system, bleed, top up pressure, add inhibitor


I've got a couple of questions, can I get that bit of black plastic back in the valve and save me the headache of bleeding the whole system?
If I do end up replacing valves is there some kind of overflow system to stop me overfilling the system? Do you leave some bleed valves open to let the air out as it fills?
Any help would be good as I don't want to leave this too long, it's cold!
 
IMG_20160223_164323.jpg
 
easier in the long run to just replace the valve (the plastic would be brittle so prob wont seal anyway)

yes

yes normally fill your system to a pressure of about 1.2bar then air a couple of rads and repeat until all rads are full
 
Thanks Shaun, I'm currently looking into a pipe freezing kit from screwfix (can't post a link as I'm a new member)
 
Thanks Shaun, I'm currently looking into a pipe freezing kit from screwfix (can't post a link as I'm a new member)
drain it down mate. Easy to freeze microbore. Also easy to defrost microbore under pressure with water running out of the radiator
 
Would be really stupid to drain the system down! Why would you do that on a pressurised system? Take the pressure off the system somewhere like a draincock and then the system is dead, zero pressure. Just tighten by hand any auto vent screws to prevent air getting drawn in and after turning the other rad valve off, remove your faulty valve and replace.
Expect some water to glug out of rad - so stuff a little bit of rag temporarily in the tail while putting the new valve on.
 
  • Like
Reactions: 2 people
Thanks for the feedback everyone.

Yes, Best, I want to avoid draining down if possible, there's the hassle and the added cost of the inhibitor etc.

So if I slowly let some water out somewhere that kills the pressure in the system right? Then I can freeze up the pipe just in case and do a quick swap.

Hopefully that will be ok...
 
Thanks for the feedback everyone.

Yes, Best, I want to avoid draining down if possible, there's the hassle and the added cost of the inhibitor etc.

So if I slowly let some water out somewhere that kills the pressure in the system right? Then I can freeze up the pipe just in case and do a quick swap.

Hopefully that will be ok...

it would be ok, but i wouldn't recommend it for a diyer as few things can go wrong, and draining down and putting fresh inh would help/ might be needed anyway
 
Can't see why you would still feel the need to freeze a pipe once you have no pressure in the system.
Good point Shaun says about the inhibitor. You might need it anyhow, although it can be injected into system if you buy the pressurised inhibitor
 
  • Like
Reactions: 1 person
Would be really stupid to drain the system down! Why would you do that on a pressurised system? Take the pressure off the system somewhere like a draincock and then the system is dead, zero pressure. Just tighten by hand any auto vent screws to prevent air getting drawn in and after turning the other rad valve off, remove your faulty valve and replace.
Expect some water to glug out of rad - so stuff a little bit of rag temporarily in the tail while putting the new valve on.

^^ This.. so much this
 
  • Like
Reactions: 1 person
Would be really stupid to drain the system down! Why would you do that on a pressurised system? Take the pressure off the system somewhere like a draincock and then the system is dead, zero pressure. Just tighten by hand any auto vent screws to prevent air getting drawn in and after turning the other rad valve off, remove your faulty valve and replace.
Expect some water to glug out of rad - so stuff a little bit of rag temporarily in the tail while putting the new valve on.
Was only saying drain as it's clearly a DIY job
 
Was only saying drain as it's clearly a DIY job

I wasn't getting at your post Riley, so don't take offence. You are right, it gets complicated for DIY. It was just that the OP seemed to think it had to be drained or froze. Seems such a waste of time and money for a sealed system.
I rarely drain any system, sealed or open vent just to change a brass fitting.
 
I wasn't getting at your post Riley, so don't take offence. You are right, it gets complicated for DIY. It was just that the OP seemed to think it had to be drained or froze. Seems such a waste of time and money for a sealed system.
I rarely drain any system, sealed or open vent just to change a brass fitting.

No offence taken mate. I am much the same. It's just if you're not used to doing it you can get a bit fingers and thumbs and that's when a mess Can happen
 
Last edited:
  • Like
Reactions: 1 person
When I was fresh out of the training centre and still an optimistic young scamp, a barefoot boy with cheek of tan, I told the fella I was shadowing about a similar job I had been offered. We discussed what he would do and then what I should do. The verdict was I shouldn't snatch or freeze as I was too inexperienced. So I drained down, which took longer but the chances of a disaster were slim.
 
On the sealed system, once the pressure is off the biggest problem will be catching water from rad.
 
Worst thing ever is snatching a new valve in and the threads don't match haha, then having to snatch the old one back in to stop it leaking while you drain down 🙁
 
  • Like
Reactions: 1 person
Worst thing ever is snatching a new valve in and the threads don't match haha, then having to snatch the old one back in to stop it leaking while you drain down 🙁

Yeah, that's what I've just done 😉

I drained enough out of the system so there was no pressure and just decided to go for the switch without the freezing. Got everything to hand, two vessels to swap out in case things went pear shaped and a big bucket.
Got both the nuts loose, stuck a make shift bung in the rad and then had that moment of 'WTH?!' (wrong sized valve)
I had a big bowl underneath and a towel and the leakage was minimal so no dramas there just the frustration of not having the problem sorted.

I will definitely drain down when it's warmer weather and I'm not dependent on having heating because the water was pretty black at times and I want to change the fill loop valve as the person who had the house before me ruined the screw head.

Back to using the immersion and electric heaters for now....
 