Increase their impedance, i.e. restrict them by partially closing their lockshield valves.What does "throttle the returns" refer to please?
It means shutting in the rad return valves (a form of balancing) or to get a quick and easy feel of what can be achieved, just throttle the pump suction valve or preferably a common return valve from "all" the rads.
Room thermostats for use with gas boilers are typically limited to a maximum of 6 on-off cycles per hour, for oil boilers this should be changed to 3 per hour. The boilers themselves will usually have their own short-cycle prevention controls built-in.When considering boiler cycling am I correct in thinking this is the total number of times the boiler turns on and off inside an hour of average running? Or how is boiler Cycling assessed in your opinions? For example at present the boiler must be firing up again about 16 times per hour. If a nozzle downsize reduced that to 10 or less then is that an indicator of a more suitable / efficient boiler size?
So the Delta temperature makes perfect sense there. It is a great influence on the heat output of the radiator. The LPM flow is calculated by the delta temp and rad size(?)This is a screenshot of the old spreadsheet that I do the calcs on and contains more info.
View attachment 72777
When downstairs is on again tomorrow I could partially close one of the ball valves on the mag filter at return line would that have same effect? Just to test temporarily. Or better to turn down the gate valve on the pump inlet instead?
I do think the boiler is oversized really. I am interested to take all readings including the hour counter measurements and compare before and after nozzle downsize.
Aka to use 2no hour counters. 0.01 hr accuracy. One connected to the circulator pump which represents the heating flow / duty time and the second to a 240v circuit on the burner. May try to measure actual nozzle firing time VS just when the boiler stat is calling.
When considering boiler cycling am I correct in thinking this is the total number of times the boiler turns on and off inside an hour of average running? Or how is boiler Cycling assessed in your opinions? For example at present the boiler must be firing up again about 16 - 20 times per hour. If a nozzle downsize reduced that to 10 or less then is that an indicator of a more suitable / efficient boiler size?
That's it, the rad size is in Kw, I just used 1kw, the flowrates are then pro rata for other outputs.So the Delta temperature makes perfect sense there. It is a great influence on the heat output of the radiator. The LPM flow is calculated by the delta temp and rad size(?)
That's it, the rad size is in Kw, I just used 1kw, the flowrates are then pro rata for other outputs.
Your pump is definitely oversized, a normal 7M pump would have done the job IMO, the old pump was knackered I'd say.
The ads are fabulous, did you know that ear wax can make you deaf?
Interesting thread. This is the kind of investigative spirit we need to have if we're really to make meaningful improvements to heating systems.
Re the infra-red thermometer, I find they work really well. However, they are usually geared to high-emissivity surfaces (it should normally explain that in the destructions). As such, any reasonably shiny metallic surface can't really be read accurately as it is a low-emissivity surface. However, there is an easy fix in that a piece of masking tape on the pipe can be used as a reliable test point.