Remeha avanta plus 28c fault code E5

View the thread, titled "Remeha avanta plus 28c fault code E5" which is posted in UK Plumbers Forums on UK Plumbers Forums.

R

royston

Hi guys,
As above, getting this code when in heating mode only. Got all the readings exact with analyser when serviced last week, as it had been doing it before service. Seemed to work alright as tested it. Then had call saying its throwing it up again.
Any ideas. Will be going back tomorrow. Cheers.
 
Have you tried the following Roy ?

[TABLE="width: 100%"]
[TR]
[TD]5[/TD]
[TD]No ionisation or ionisation failure more than 5 times during one heat demand.[/TD]
[TD]CO[SUB]2[/SUB] wrongly adjusted [/TD]
[TD]Check:
• CO[SUB]2[/SUB] adjustment on the gas block;
• ignition/ionisation pin;
• flue/air-supply connections;
• gas flow at full load;
• if there is no recirculation of flue gasses (either inside or outside the boiler).
[/TD]
[/TR]
[/TABLE]


Does it work fine with the case off ?
 
Usually it is wrongly adjusted co2 check flue terminal clear however also gas supply ok /gas pipe sizing correct and working pressure at boiler ok even when other appliances on/in use

Had one intermittently going to e4 the other week,turned out gas isolation at meter not fully open and when gas cooker used pressure drop caused fault
 
Could be electrode requires cleaning or changing, also check inner burner seal, available as a service kit, electrode & allburner seals
 
replace the ignition electrode and the ignition box, that will sort it , had that a lot in the preston area

Hope this helps
 
Hi, was wondering how you got on in the end with that Remeha Avanta boiler showing the E5 fault. I have one starting to do the same thing. I changed the electrode and corrected the O2/co2 ratio but still not firing occasionally. Left it working on Friday and the customer said he would contact me again on Monday (hopefully with good news!!). Any help would be appreciated.
 
how did you guys get on with the E5 fault? Ive had one recently, done everything it says from checking the co ratio etc, ionisation etc...spoke to remeha and they say its the gasket in the main burner which my local parts centre can only sell me in packs of 20 from the manufacturer...and i dont envisage getting another 19 remeha E5 faults!
 
Hi guys,
As above, getting this code when in heating mode only. Got all the readings exact with analyser when serviced last week, as it had been doing it before service. Seemed to work alright as tested it. Then had call saying its throwing it up again.
Any ideas. Will be going back tomorrow. Cheers.

Hi I have had this error lots of times and every time I have replaced the ignition transformer and it's sorted the problem
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Remeha avanta plus 28c fault code E5" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
royston,
Last reply from
Ermintrude,
Replies
14
Views
11,161
Back
Top