Just remember drains need to be air tested , but once test is done the vent pipes open to atmosphere, same with air test, certain parts will get covered and uncovered,
 
Depends on the fire, Fluless, Conventional, LFE, DFE and the Mi's instructions. Some of the DFE's require 100cmsq regardless of the 7kW. BS5871 parts 1 to 4.
 
  • Like
Reactions: 2 people
And page 76 to see what needs to have been done to get anywhere near 5M3/h/M2

Good point SH, but the main thing is to be aware of the requirements, and in a new home ascertain the degree of air changes. Have you not noticed that fireplace openings are now often boarded over?
 
Last edited:
Refer to section 1.4 in part F. Part F must not be read in isolation of other building regulations such a part J.
 
I was always told under 7kw need no vent UNLESS evidence of draft proofing. New houses are sticky because I always asked what's a new house? 2 year old, 5 or 10. Regardless of bs, MI always over rule anyways.
 
Refer back to post 22. For instance: BS5871 part 3 section 8.2 100cm2 ventilation shall be provided unless manufacturers state otherwise. There is ventilation for breathing and ventilation for fossil fuel burning appliances; they are two different things.
 