Barry98
am a tad stuck on my pet hate (so called engineers that run round saying change the pcb change the pcb) im sure i am wrong just not as to why.lol
i have a rd 532 (which i think is a rebadged worchester bosch) fault code EA which raeds " is gas cock turned on ? check - supply pressure , power supply , igniter electrode and lead , ionisation sensing electrode, flue duct and co2 level.
now iuve checked all these but i can not see where the ignition sequences is failing as the boiler will not re-set.
it also says more detailed fault finding are described in the service booklet for engineers , number 181 465 346
anyone wanna chuck some ideas at me . ive only ever replaced 2 pcb in all the years of doing this but this one has me beat.
im feeling bad cos the guy is 83 and BG got him to take this boiler on finance as his old was buggered by all acounts.
cheers boys and girls