Guest viewing limit reached
Supporting pipes under floorboards + insulation
View the thread, titled "Supporting pipes under floorboards + insulation" which is posted in UK Plumbers Forums on UK Plumbers Forums.
Needs clips every meter and lagging
agreed about the lagging -
No sag is acceptable the lazy scrot, should be clipped every 0.5m minimum for horizontal run in 22mm.
See page 19.
Perfect, thanks! I’m using a registered gas engineer so never expected this 🙁
Besides the manufacturer‘s spec, what / where are the building or other regs that installers should be following?
also, from a trade perspective, what is a customer’s recourse when work doesn’t meet regs or standard? It strikes me that a lot of work could / should be checked by an independent, or at least recorded as proof of continuing competence.
[automerge]1604740603[/automerge]
...and btw the fitting isn't necessary leaking because it's faulty. It's more likely to be leaking because the pipe isn't properly seated and or the fitting is under stress because of the lack of support.
totally agreed, and also, no idea how my plumber expects to be able to drain the ground floor.
it gets worse really as I removed the floorboards and can see that other (15mm) pipe is only supported by a partition wall and - no kidding - an electric cable.. see attached pic.
No pipe lagging under a floor void big no needs insulating
sorry, do you mean it does or does not?
The pipes are feeding three radiators, each 1.5kW, so I can see the case that at max demand the flow is high enough that piping heat loss is relatively low, but at lower flow does insulation make that much difference?
Have a look at building regulations part L insulation is a necessity needed for thermal efficiency and for frost protection
British Standards BS6700:2006
Design, installation, testing and maintenance of services supplying water for domestic use within buildings and their curtilages.
Maximum spacing of fixing for internal piping
PB or PEX pipe
clip spacing = horizontal/vertical
Up to 16mm diameter = 0.3m/0.5m
18 to 25mm diameter = 0.5m/0.8m
Reply to the thread, titled "Supporting pipes under floorboards + insulation" which is posted in UK Plumbers Forums on Plumbers Forums.
kasser,
gmartine,