Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Matt0029

Gas Engineer
Oct 6, 2017
1,245
110
63
37
leeds
Member Type
Heating Engineer (Has GSR)
What can be causing a temperature relief to drip. I have recharged the expansion vessle that had totally lost its charge. I am g3 registered. Thanks
 
I would fit one and see

Shaun I advised to isolate cold main into cylinder, drop some pressure out and then see if the PRV started to drip again after enough time for any back feeding to accumulate and it didn't happen, so installing a double check valve is not needed to test correct?
[automerge]1583332686[/automerge]
I may put a pressure reducer on the main in coming pipe and set to 3.5bar. So it's balanced everywhere.

I would advise one under the kitchen sink on incoming main so as you say it's all balanced, although this is not the current problem
 
Shaun I advised to isolate cold main into cylinder, drop some pressure out and then see if the PRV started to drip again after enough time for any back feeding to accumulate and it didn't happen, so installing a double check valve is not needed to test correct?
[automerge]1583332686[/automerge]


I would advise one under the kitchen sink on incoming main so as you say it's all balanced, although this is not the current problem

might of caused the original problem tho me and you know they don’t seal good after they’ve discharged

I would say prv on incoming one size larger eg 28mm for a 22mm supply etc

and change the incoming block
 
  • Agree
Reactions: SJB060685
I've never had any issues with them sealing after opening - it's clean water, in theory no rubbish should get under them and thus seal OK.

I've only ever had three fail (where the Expansion has been OK) has been on temperature. One dripped on temperature rise and the other two would open full bore on a temp above 45oc. The other issue is backflow but that seems to have already been discussed.

Daft question - but are you sure it's the Temp/Pressure Relief valve dripping. Many installers tee that in with the blow off from the combination valve before the tundish - could it be this dripping instead? I find more regularly these fail.
 
I've never had any issues with them sealing after opening - it's clean water, in theory no rubbish should get under them and thus seal OK.

I've only ever had three fail (where the Expansion has been OK) has been on temperature. One dripped on temperature rise and the other two would open full bore on a temp above 45oc. The other issue is backflow but that seems to have already been discussed.

Daft question - but are you sure it's the Temp/Pressure Relief valve dripping. Many installers tee that in with the blow off from the combination valve before the tundish - could it be this dripping instead? I find more regularly these fail.

It's the 6 bar expansion relief valve that's the culprit, not the combined pressure and temperature valve mate
 
  • Like
Reactions: EvilDrPorkChop
It's the 6 bar expansion relief valve that's the culprit, not the combined pressure and temperature valve mate
Ah yes, I read the first post and skim read the rest!

I'd put it down to a faulty 6 bar blow off then, easy enough to replace without replacing the whole combination valve. Had plenty of them fail for no apparent reason, probably most likely from the expansion not working correctly previously.
 
  • Agree
Reactions: SJB060685

Official Sponsors of Plumbers Talk

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.