T
Tom Jackson
18m of 2"
10m of 1.5"
10m purge hose of 25mm nominal bore
U40/G25 meter installed
Please calculate IV and PV and Purge Time
show your workings so i know youre not using your app!
point in this being i keep getting it wrong according to app but know im right!!!
Worked in gas since i left school at 16 for transporter, currently doing commerical gas metering for them
Interesting first post Tom. Care to introduce yourself?
His name is Tom....... and like me doesnt believe in apps to work things out 🙂 but I dont do commercial so cant help, he needs croppie or Tamz using their abbacus to calculate the answer.
Reactions: 2 people
Couldnt resist a chalenge
Is it
PV 0.247m2
Pt 3min 20sec ish
(3600(1.5((0.0024×18)+(0.0015×10)+(0.00064×10))))÷4.5
:46:
my app says:
Pipe IV: 0.054200
Pipe PV: 0.89430
Total PV: 0.199030
Purge time: 159s
I used TPCP1A and would have to chk workings
Does TPCP1 have different outcome?
I make it
Ivm -
U40 meter - 0.067m3
Ivp -
2" - 18 × 0.0024 = 0.0432
1.5" - 10 x 0.0015 = 0.015
0.0432 + 0.015 = 0.0582 m3
Ivf -
10% of Ivp = 0.00582
Iv total
0.067 + 0.0582 + 0.00582 = 0.13102 rounded up = 0.14m3 installaton volume
Purge
pv of meter = 5 x 0.02 = 0.1 m3
Pv of pipework 1.5 x 0.0582 = 0.0873 m3
Pv of purge hose 1" - 10 x 0.00064 = 0.0064. 1.5 × 0.0064 = 0.0096 m3
Total purge volume 0.1 + 0.0873 + 0.0096 = 0.1969 m3 rounded up to 0.2 m3
Purge time = minimum flow rate for 2" is 4.5 m3h
0.2 x 3600 ÷ 4.5 = 160 seconds
Any good?
And at half 3 in the morning following 3/4 a bottle of jura i'll be fu kd if i';m gonny work it out 😉