O
Oddbod
I'm not a heating engineer and I have no intention of touching our boiler, but I really could do with some friendly advice regarding a weird fault.
The boiler is an 8-year old ThermeconS90/120. Burner is an Ecoflam Minor 4. Nozzle is a 1.10/60 Location is a dry outhouse.
When cold the boiler will fire with a flame established, but almost immediately locks out. Press the lockout button and the boiler fires and behaves normally. The fault only seems to occur when firing from cold. Any residual heat and things work fine.
What follows is the history. I'm not being critical of any of the engineers actions – the detail is just there 'cos I don't know what matters and what doesn’t.
The boiler was working perfectly until it was serviced. The nozzle was replaced however the port normally used for the air supply probe could not be used as something was “spinning around” (I assume the plug screw or connector thread stripped?). The engineer drilled a hole in the flue but then found he didn't have the right sensor equipment so didn't set up the air supply. There was no black smoke from the flue so it was deemed OK. He didn’t seal the hole in the flue.
Following the service there was a tiny continual oil leak from a connection - a drip an hour kind of thing.
After a week the fault started to occur and the engineer came back, cleaned the nozzle (it being sooted up) and set the combustion mixture using the hole in the flue for the sensor. It took a long time and the air setting ended up much higher than the manufacturers suggested range (and much higher from what it was when the boiler was working before the service)
It worked fine for a week and then the fault started to reoccur. The engineer stopped taking my calls.
I found a second engineer – really nice bloke, well recommended and clearly knew oil boilers.
The second engineer performed another service. Fixed the oil drip, cleaned out the baffles which were full of red powder and set up the combustion. Didn't change the nozzle.
A week later the fault reoccurred.
The engineer returned and replaced the nozzle. (On the grounds that the first one may have been faulty since it was the only thing replaced since the boiler had worked). Set up the combustion again, ending up with the air setting much nearer to the recommended value this time.
This morning the fault reoccured.
Before I ring him again I'm just wondering if anyone has any great ideas we could check out. This has all the makings of a “just throw bits at it 'till it works” saga. Which is fine if that's all we can do, but I'd feel daft if I hadn't at least asked if this problem rings a bell with someone.
Following are some additional points.They may or may not be correct.
The boiler was working fine until the service, so something happened at that point. The first engineer inadvertently damaged or changed something or otherwise provoked the fault – photocell, wire, control board? (I'm not having a pop here, I know that coincidence happens and that the slightest disturbance can exacerbate an existing fault. That said I do now wonder how experienced the first engineer actually was.)
According to the second engineer the photocell is clean and seems to be in the right place.
The oil tank is pretty full. It was not topped up, the supplier was not changed etc. The oil pressure and filter seem fine.
The solenoid seems to be OK (it seems they usually fail when hot not cold).
(See, I now know far more about oil boilers than I ever thought I would!)
So I have two questions. Is anyone thinking “Oh yeah, that's obviously.......”? Secondly would it be worth replacing the whole Ecoflam burner. I believe it's a couple of hundred pounds and, provided the fault is somewhere in the existing burner, it wouldn't take too many more visits for that to become the cheapest option – let alone the most convenient one!
Thanks for any advice.
Oddbod
You say the filters seem fine, are they? is it gravity fed? Is there plenty of flow flowing to the burner on it's own accord?
Hi Croppie,
Whenever it has been off for 7 or 8 hours. So mornings and evenings both. Its Ok if it's only been 2 or three hours.
Hi MarkOil,
As far as we can tell. The boiler has a pump but the tank is higher than the boiler and when it runs out (ahem first winter - 3 years ago) it self primes fine.
You thinking that the pump might be "lazy" and needs a couple of goes? The odd thing is that the flame establishes but then the lock out occurs. It doesn't seem like oil starvation.
If cold start ONLY it fails after flame ignited, then it is your engineers fault, - simple as that. Get an engineer to make sure burner is set correct. Did you get the air adjustment that was broken fixed?
How can you be sure it is now occasionally failing only on cold start? It could go to lock out previous night unknown to you.
Sorry chaps, still on pre-mod - so replies need to await approval. (And thanks to the mods for taking time out to do so.)
Hi Best,
We've set the burner a total of three times, by two different engineers. It runs fine for a few days and then the fault re-occurs. No re the adjustment, neither engineer seems to think it matters and they both used the hole drilled in the flue. Whats broken is whatever the engineer would normally remove to stick the probe in.
Once started it seems to run fine until the time clock shuts it off. I can hear it fairly well. It never seems to lock out during an "on" period. That said I will check tonight & make sure. Fair point.
^^^^ I concur.
If they left a print out of your flue readings can you tell us what the O2, CO2, CO and flue temps are?
Agree with all that has been said
also could be filter and after it is primed after first lockout will carry on all day. Just done one today same problem
Thanks for all the advice.
Hi Best, I confirmed that it locks out on start not the evening before. 60degree is the recommendation in the manual, but we don't know what the first, working nozzle was. Stupidly I threw it away. What would you try?
Hi Croppie, No I don't have a print out. Are you saying I should have had one? If so I will ask next time
Hi SimonG, seemed to be up to temp. The boiler thermostat was on max and it had been burning constantly for a good 10 mins by the end of the setup.
The consensus here it that it is over-aired. So on the basis that a consensus is a consensus for a good reason that sounds like the place to look.
What puzzles me is how two engineers could set it up wrong three times. It's not like it's an unusual procedure. Could something be drifting or moving? An air leak somewhere? The sensor is being placed in the flue rather than close to the burner. Could that throw the figures out?
Kimbo, we might as well try replacing the filter too this time. It can't do any harm.
Guys, I really do appreciate the help!
Oddbod
Filters are checked as part of a service, so is analysis of the flue gases to give you flue temp, xs air, o2, Co ppm, CO2, efficiency etc, of which all would be filled out on a cd/11 form:
[DLMURL]http://www.ossw.co.uk/wp-content/uploads/2011/10/Commissioning_form_CD11_web1.jpg[/DLMURL]
From this they would probably diagnose the problem straight away (if they understand the readings)
From their analyser they should also be able to print a hard copy of the readings from your boiler for them and you to keep.
If they haven't done these then they haven't serviced your boiler or correctly or looked into the fault properly in my eyes, or OFTEC or other engineers I wouldn't of thought.
Maybe get 50% off all that you have paid so far for half a job done?? Just a thought.
Thanks MarkOil. He definitely used the gas analyser but didn't leave me with a printout. I'm an engineer myself - albeit an R&D one - so we were chatting about what he was doing and about the mechanics of boilers as he was setting it up. He was focused on juggling the CO and C02 - it was very sensitive. If he was faking it was a good act!
More worryingly I can't find either the engineer or firm on the Oftec registered list, despite the Oftec logo being on the website. At least he's not on the list of the 4(!) engineers who have had their membership revoked. Think I'll give Oftec a ring - make sure I'm not misreading their membership list or something. If He's legit we'll have another go. If not I'll do what I should have done in the first place and find someone who is on the Oftec list. Live and learn I guess.
1st engineer sounds a real cowboy, didnt clean baffles, cleaned a nozzle (!), got FGA wrong.
Drilling the flue is fine if the test point is seized or unserviceable but should stick a bolt in it afterwards.
As above, over aired can knock the flame off but also worth checking the ht leads arn't obscuring the photocell, that can create intermittent faults as can worn ht leads, maybe the cold mornings are a red herring.
Thermecon 90/120s are temperamental beasts at the best of times. To get any decent figures, stick in an 80° EH nozzle at minimum rating. It is very hard, if not impossible to get good figures with a 60° nozzle as the flame hits the back of the combustion chamber.
Is the flue conventional or balanced? A long balanced flue on these can cause problems.
Other possible causes for this type of intermittent failure are the motor capacitor (but this will have been tested during the service) the motor itself, or a tight point on the oil pump.
Reactions: 2 people