A piece of 5mm flat bar bent at 90 degrees can scrape almost anywhere in the combustion chamber. Drilling a hole in one end for a 8mm bolt makes a great leverage tool for getting out those pesky wb camray baffles.
 
I am currently on the Oftec-50 and am grateful for tips like this as to what to take on a job.
 
Coils.
Danfoss state their operating range is 1.8 - 2.2 KOhms (across the 2 facing terminals).
If you suspect the coil is your intermittent problem, check the resistance when its been running for 10/15 mins - if the resistance is increasing, ie up to 2.5 or 2.6 then bingo its about to give up the ghost.

Maybe a very silly question.......but......do you test this while it's still energised and connected to power?!!

I imagine the figures you posted above (RDB Coil 90 - 100 Ohms) is with the coil disconnected?
 
So the post I quoted from Bunker where he said to test the coil after it's been running 10-15 minutes, to see if the resistance is climbing, that is also with it de energised?!
 
Probably he meant to say test it isolated when its was warm after it has been in use
 