TRV Continuously Shutting Radiator Off
View the thread, titled "TRV Continuously Shutting Radiator Off" which is posted in UK Plumbers Forums on UK Plumbers Forums.
A
Associate
Hello,
Sorry for the long post, but I think detailed information will help you in providing maximum input!
I live in a 3 bedroom, 2 floor (Ground, 1[SUP]st[/SUP], 2[SUP]nd[/SUP]) end terraced house, with 7 Gas Radiators in the property. The house is 30 years old.
Previously we had an old system where there was no separate control for Heating and Hot Water; so whenever the boiler was turned on, it used to heat up the water and the gas radiators at the same time.
That boiler was a Micron Glow-Worm 50FF, which we had for over 10 years.
All the Radiators had TRVs on them, and they used to work perfectly well. The property did not have a Room Thermostat though.
Recently (beginning of last week), we had a brand new Baxi 18HE A Boiler installed, along with 3 x radiators (the 3 being replaced were old and had pin holes in them), and new pipe work ( 2 primaries), which meant that Heating and Hot Water could be separated, and they could be controlled separately, on behalf of an Energy company by subcontractors, as part of the Government’s ECO legislation.
So the new system we have now is a Y Plan Sealed system (although with the old system we had an Expansion Vessel up in the loft).
The water and heating has been absolutely fine and we have familiarised ourselves with the new system without any problems, including the Room Thermostat.
Just to clarify please, the problem we are having is not related to the Room Thermostat, the Settings of the Digital Programmer etc, or our lack of understanding of the Room Thermostat, Thermostatic Radiator Valves or anything else.
2 out of the 3 new radiators are working fine as are the other 4 (old) radiators.
However ,there is a problem with one radiator (TRV), which was newly installed. The TRV on the radiator was brand new too.
When this radiator was turned on, just like the other radiators it came on and got warm, but used to then shut off permanently, without coming back on, while the other radiators continued to stay on throughout.
This particular radiator after reaching a certain temperature/warmth, just shut off and stayed off; even for hours without coming back on, while the Heating was still On and the other radiators remained on and remained warm.
If the TRV head is removed from this Radiator and Heating turned on, the radiator remains. I recently monitored it closely and kept the Heating on for a continuous 18 hours, and this radiator, without TRV head on, remained on and hot for this whole time.
When the Engineers that carried the work returned to our house they were baffled, saying a radiator should either come on or it shouldn’t, and to go off after a while (within 30 mins or so) after coming on didn’t make sense. They also realised that none of the other radiators were doing this, and only this particular radiator was showing this fault.
They changed the TRV Head and screwed it on loosely (which I later realised), making it appear that everything was working fine as the radiator stayed on constantly and didn’t shut off. But after I turned the TRV Head on and off, it came off, due to not being securely screwed on.
So, if the TRV Head is left off the radiator completely, the radiator stays on constantly as soon as the Heating is switched on. If the TRV Head is put on loosely – when you can just about turn it on and off before it would eventually fall off – the radiator would stay on.
I lost confidence in the Engineers that carried out the work, as I found their conduct unprofessional throughout and felt they lacked integrity, especially as they showed little consideration about the fact that I had an elderly and disabled mother in the house.
I invited a friend of mine, who is Gas Safety Registered, to have a look at it, and we both agreed to begin with (I was especially keen to get some clarity and eliminate as many “possible” causes as there may be for this) that it would be a good idea to replace the whole TRV – TRV Head & TRV Body.
I wanted a brand new Danfoss TRV. After draining the radiator etc, he fitted the Danfoss TRV onto this radiator.
It soon became apparent that the radiator with the new Danfoss TRV on it was doing the exact same thing as before – it would come on, and after reaching a warm temperature, it would just shut off and stay off within 30 minutes of being turned on (less really), while the other radiators remained on and remained warm. So, the original (brand new) TVR Head & Body that were fitted to the new radiator in the firt place weren't faulty.
Just want to point out that this radiator in question is on the first floor, just above the Boiler on the ground floor kitchen.
My friend said that he had never come across anything like this.
His “theory” was that the pipes for this radiator were getting particularly hot and so was the radiator, quite quickly due to being directly above the boiler. He said that the Thermostatic Head was obviously “sensing” this temperature, finding it exceedingly hot and shutting the radiator off. He reduced the Heating temperature on the boiler and restricted (closed it quite a bit) the lockshield valve on the opposite side to the TRV. Neither of these things made a difference.
As quite an experienced and well respected Gas Engineer (Gas Safety Registered), he had never come across a situation like this and was at bit of a loss. His final suggestions were to consider replacing it with a Half Turn Valve (non thermostatic), as that will come on and off whenever we want and not be like the current one because of different technology.
His second suggestion was to move the TRV to the other side of the radiator, where the Lockshield is, and switch them around, in relation to something “technical” to do with the return pipe, but there is no guarantee this would work.
Hope you are still with me and I haven’t exhausted you by waffling too much!
*Does anyone know what is going on and why?
*Are the 2 options my friend suggested the only ones available to me?
I’ve been getting quite stressed about everything, which has upset my vulnerable mum too.
Thank you.
:smile5:
sound like faulty valve to me. they should replace it as changing head won't really help. can you move the pin freely up and down? call them back and ask them to replace trv. As you said they haven't tightened head on properly so it looked like its working but in fact trv was fully open.
It's done it with a new valve as well though. I'd go with swapping ends initially and see how that works. Failing that a remote sensor TRV may be the solution.
Agree swap side of radiator first. Is the room with the suspect trv exposed to another heat source? Ie fire, wood burning stove or is it exposed to direct,sunlight?
Or is it in an enclosed corner or in a radiator cover?
a photo would be a great help
Or may be its doing its job properly and turning off because the room is warm enough.
The room with "suspect" TRV is not exposed to another heat source.
In fact this radiator (1400 x 450) in the bedroom, which is
about 15 sqm in size, is right next to the window (directly below
window ledge). It's at the end of the room, centrally located.
I don't know if this information helps, but this radiator
is one of the 3 that was replaced (1400 x 450), and the previous radiator was about 1400 x 600 in size and 30 years old.They put this size in for their own convenience
really, as the subcontractors including material order/delivery
was all over the place.
Although, the system (pipe work), boiler and size of radiator (don't know if relevant) previously
was different, in the same room, under the same conditions, we never
had any problems with the old radiator or the TRV - always worked
perfectly without any problems.
Also a 3 Port Valve has been fitted above the new Baxi boiler.
The Airing cupboard is on the 2nd floor (top floor, opposite side of the bedroom in question). This is where the Cylinder is. The Automatic
Bypass that was fitted is in here as well.
The new Danfoss TRV that has been fitted is Bidirectional.
The system wasn't balanced by them when they completed the work, but was after
they revisited. Made no difference to this radiator in question.
My Gas Engineer mate also addressed the balancing issue again, but the problem with this radiator continued.
Rather than get stressed why not let your mate swap the stat to the other side see if that resolves it ... If you need it to be thermostatic you can get a TRV with remote sensor that fits away from the radiator.
Like the above post.
Forget how hot the radiator is. Is the room up to about 23 to 25 degrees. If it is the trv is doing its job.
Looking at the pictures it could just be the heat rising from the pipes below causing the trv to shut. Try wrapping an old blanket around the pipes to insulate them and see if it makes a difference.
If it does then you are looking at fitting a TRV with a remote sensor or insulating and boxing the pipes.
Try swapping the head of any working rad with the problem one.
Does the problem follow the head?Could be a batch of faulty TRV heads.
What setting do you have the valve on? if its max may as well remove it.
Put a thermometer near the TRV to see when it shuts down and opens.
Lastly an external TRV sensor as the pipes across skirting boards giving extra heat around trv.
This is another piece of advice someone gave me:
[FONT=&quot]"take the head off, the valve has a grey knob just underneath the pin with two arrows on it, if the pipe with the valve gets hot first then the arrow should be up on the mark, if it's the other pipe that gets hot first then turn the knob so the arrow faces down on the mark, re-fit the head[/FONT]"
[FONT=&quot]I fiddled about with the grey knob (although my action was a lot more amateur), and this radiator "seems" to be working ok now. I'm still going to be monitoring it, but hopefully there will be no need to revisit this again.[/FONT]
[FONT=&quot]
Thank you everyone for your input :smile5:[/FONT]
[FONT=&quot]
While I'm able to benefit from knowledgeable and helpful folks, I hope I can ask one quick question please!
The radiator in the hallway where the Room Thermostat is doesn't have a TRV on it (as recommended), and has a Lockshield on that side instead, so as soon as the Heating is turned On, this hallway radiator is constantly On.
*By the way, there is an Auto Bypass fitted in the Cylinder Airing Cupboard.
I wanted to know, will it be ok to replace the Lockshield Valve with a Half Turn Valve (non thermostatic), so that this radiator can actually be turned off (my mum would prefer this, as all the technology - Room Stat, Digi Programmer - is a bit confusing for her, and having bit more "control" over this rad will make her feel more at ease, and I just want her to be happy) without this having a detrimental affect on anything?:
Thank you.[/FONT]
Assuming the room stat is in the hall that rad should be left on as it is providing the overall control to the system. If the hall rad is turned off the hall may not reach the set temperature and leave the boiler chugging away with all the other rads shut down by the TRVs. This will waste energy and potentially shorten the life of the boiler.
NEED FURTHER HELP PLEASE!
Just realised that there is a problem with the ground floor hallway radiator, where the Room Thermostat is, and the first floor bedroom radiator. Both of these radiators are a few years old but were in perfect working order before the new boiler and pipes (to create separate controls for Heating & Hot water) were installed.
As I previously stated, the hallway radiator has got a Lockshield fitted instead of a TRV, which is the recommended way, as confirmed by posters on here. This is the only new work carried out on this ground floor hallway radiator.
However, when the Heating is turned On, the hallway radiator and the bedroom radiator (TRV fitted) come On only when other radiators in the house are turned On. All these radiators (5) have got TRVs on them. The Hallway and Bedroom radiator never come On on their own, without us turning On other radiators in the house.
It appears if any, even 1, of the other 5 radiators in the house are turned On, these two radiators will come On and the pipe underneath them gets hot.
If all the other radiators in the house are off, and we only want the Bedroom radiator or the Hallway radiator to be On (which is supposed to be the case as soon as Boiler Heating is turned On, due to it having a Lockshield), you can hear these 2 radiators making a noise – the sort of noise radiators make when they are On – but they don’t get hot, and the pipes underneath them don’t get hot either.
The Bedroom radiator (TRV) and the Hallway radiator (Locksield) will only come On if the other radiators (at least 1) are turned On. Then both come ON and get adequately warm.
The Hallway radiator’s “opening” & “closing” valve on the other side, that is used to balance radiators, is fully open. The Bedroom radiator’s valve is open too, but not fully, to help the balancing process, but isn’t severely restricted.
Rest of the radiators in the house seem to be working fine.
All radiators have been balanced.
Just bit more information in case it is relevant – the boiler is in the ground floor, in the kitchen. There is a radiator in the kitchen that is about 310cm away from the boiler. The ground floor hallway radiator is about 420cm away from the boiler.
There are 2 radiators on the ground floor – Kitchen (new radiator
installed with boiler) & Hallway
2 Radiators on the first floor – Bedroom & Living Room (new radiator)
3 radiators on the 2nd (top) floor – 2 x Bedrooms & Bathroom (new radiator)
Just more frustration, but I’m trying to remain calm. I’d rather get input from you guys first and actually have more faith in you, before calling out a Gas Engineer to be honest. Please read my other posts in case they help with this.
Any ideas what the problem may be and what I could try please?
Thank you.
Without ripping floors up it sounds like there's piping issues, maybe radiators fitted in series, God know's why? OR you have some serious circulation issues (less likely or improbable)!
Are you sure they worked fine before hand? If so then I'd be wondering what the installer has done since to bring about such a change in the system?
Yes, all the radiators worked perfectly well before. The new installation included 2 Primaries - separating the Heating and Hot water control. To do this, they ran about 24 meters of 22mm copper pipe from the ground floor kitchen boiler, through the ground floor hallway, then up to the 2nd (top floor) Airing cupboard, where the Cylinder is. (This is what they told me they would do anyway!).
They didn't touch the bedroom radiator we are having problems with now. They only took off the TRV and replaced it with a Lockshield on the hallway radiator.
We are only having these issues with these 2 radiators. I don't know if this is relevant, but the ground floor hallway radiator and the first floor bedroom radiator, as well as being on different floors, are located on opposite sides of each other. So the hallway radiator isn't directly below this bedroom radiator.
I can't say the installers were the most competent or professional, but I'm also wondering what they could have done to cause this, because we definitely did not have these issues before.....
When the heating is turned on, all radiators will heat up. When a room reaches the temperature set on the TRV, the TRV will control the flow through the rad to maintain the required temperature. When the hall reaches the temperature set on the wall thermostat, the boiler will go off.
Is someone (your mother?), going round the house turning the TRVs up and down when they are using/not using a room in an effort to save fuel?
Very badly by the sound of it.
If you want to have a go yourself, here's how you do it:
[TABLE="class: forumline, width: 100%"]
[TR]
[TD="class: row2, width: 100%"][TABLE="width: 100%"]
[TR]
[TD="colspan: 2"]1. Remove all TRV heads and set all wheel valves to fully open.
2. Set all lockshield valves to 1/3 of a turn open from closed (fully clockwise).
3. Allow the system to heat up.
4. Feel all return pipes (cooler one) to see how warm they are.
5. Select one which is midway between hot and cold and use it as a 'standard'.
6. Any rad with a hotter return than the 'standard' should have the LS valve closed a tiny fraction.
7. Any rad with a cooler return should be open a tiny fraction.
8. Repeat 4 to 7 until you are satisfied with the result.
Do no expect perfection. The adjustment each time is very small and you need to leave time (say 10 mins) between step 7 and step 4 for the system to settle down.
When finished replace all TRV heads and set to required temperature. Set all wheel valves to required position.[/TD]
[/TR]
[/TABLE]
[/TD]
[/TR]
[TR]
[TD="class: row2, width: 150, align: left"][/TD]
[/TR]
[/TABLE]
Could be a one pipe system that has been adapted incorrectly?
how old is the original heating pipework?
[To answer "doitmyself," no one is going around the house adjusting the TRV's on the other radiators. It definitely isn't a Room Thermostat issue either, whereby we are confused about how the Room Thermostat works. I will bear in mind the advise on balancing. Thanks. ]
The original heating pipework is 30 years old, same as the house.
It's been piped wrong. Get the installers back but on Eco you'd have more luck picking 123456 for Saturdays lottery.
Would you say it's been piped wrong by these new installers, and nothing to do with the original 30 year old installation (all radiators worked fine before new work)?
If so, for my own reference, any "ideas" (I know it's going to be vague without you inspecting in person, but even your and other members' "educated guess" would help me) what they might've done wrong?
Thank you.
Then what do you mean by: "If all the other radiators in the house are off, and we only want the Bedroom radiator or the Hallway radiator to be On?
The only way you can achieve that is to turn off the unwanted rads at the TRV.
To clarify, when we wake up first thing in the morning and the Heating/Boiler is off and all radiators TRVs are off, and when the Heating is turned On we only want this particular Bedroom radiator or Hallway radiator to be On. So from beginning of day and from the moment the Heating is first turned On, no one is going around touching the other radiator TRVs.
Unfortunately, there is a strong chance this may be the case.
If I want to hire a Gas Engineer privately to rectify this, any ideas how much this will cost as an estimate, as I am based in East London (minimum to maximum)?
Would a Gas Engineer who is correcting this problem need to buy any additional parts for this?
Thank you.
This is the type of thing that need a visit to properly diagnose.
Put a post up in this bit
[DLMURL="http://www.ukplumbersforums.co.uk/im-looking-plumber-gas-engineer/"]I'm looking for a Plumber or Gas Engineer[/DLMURL]
There are a few good lads on here in your neck of the woods who could get you fixed out.
More than a tenner and less than 5k :smile: No one can give you a costing, even vaugely until they see what is involved but you won't be ripped off.
Of course they may need to buy parts but probably limited to pipe and fittings.
Thank you for all your help guys!
I will take everything on board.
I just wanted to ask for my own reference- if we didn't
get anyone to rectify this fault and left things as they are,
apart from the inconvenience, could this cause any long term
problems or damage to the system if we leave things as they are?
The radiators will have cooled down overnight, but that doesn't mean they are off. If the TRV has not been touched, i.e turned down to the lowest setting, the room will warm up, when the heating is turned on, until it reaches the temperature set on the TRV.
Reply to the thread, titled "TRV Continuously Shutting Radiator Off" which is posted in UK Plumbers Forums on Plumbers Forums.
Associate,
doitmyself,