Unvented cylinder in loft with open vented heatinf

View the thread, titled "Unvented cylinder in loft with open vented heatinf" which is posted in UK Plumbers Forums on UK Plumbers Forums.

I have a job putting an unvented cylinder in loft, (I’m G3) but they have open vented heating. I’m wondering if this will be possible as flow into cylinder will be higher than f and e tank. Worries about pumping over, any thoughts? Convert heating to close system first?
 
Sealing the system is not the only way. You could lift the F & E tank above the cylinder. Sealing a system is all well and good but not the only way and not always an option.
 
Sealing the system is not the only way. You could lift the F & E tank above the cylinder. Sealing a system is all well and good but not the only way and not always an option.

I agree you could raise the tank above the cylinder if theres room but I suggested sealing it because hes in the loft anyway and might as well do away with it and free up some space.
 
I agree you could raise the tank above the cylinder if theres room but I suggested sealing it because hes in the loft anyway and might as well do away with it and free up some space.
Ive installed sealed heat pump systems and others with a plate and many other variations and configurations. I was mere pointing the (sealing the system) was not the only way
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Unvented cylinder in loft with open vented heatinf" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
MethodPH,
Last reply from
SJB060685,
Replies
7
Views
1,596
Back
Top