Yeah you can use the same live, you don't need separate lives for each valve.I am no sparks , is it acceptable to use the one perm live and split to supply both 2 ports ? Assuming there is one lol
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Yeah you can use the same live, you don't need separate lives for each valve.I am no sparks , is it acceptable to use the one perm live and split to supply both 2 ports ? Assuming there is one lol
Yeah you can use the same live, you don't need separate lives for each valve.
Isn't as simple as that unfortunately. As the HW Stat on a 3 port fires the boiler when it's just HW only. If the heating was running on the 3 port (So Live on the Orange wire on the 3 port) , it would back feed and hold the HW 2 port valve open. Therefore defeating the object of a thermal cut out.wire the port valve into the stat but you need a neutral
Isn't as simple as that unfortunately. As the HW Stat on a 3 port fires the boiler when it's just HW only. If the heating was running on the 3 port (So Live on the Orange wire on the 3 port) , it would back feed and hold the HW 2 port valve open. Therefore defeating the object of a thermal cut out.
As the HW Stat is wired to fire the boiler (HW on to Common on stat, then 1 to S/L on boiler). Then the Orange wire for CH only on the 3 port is wired into the boiler at the same terminal (So your S/L on the boiler). So when you wire your additional 2 port into the 1 terminal on the HW stat (So that the 2 port closes when the stat breaks) if there is still a feed on the S/L to the boiler from the heating side the 2 port valve would still have a live feed and stay open.
Yeah, and the stat out also would have to go to boiler S/L. So if your S/L on the boiler is live from another source, so the heating. The valve would still be live and hold open.no it wouldnt
perm live to stat in
stat out to brown eg port valve open
neutral and earth the same done
Yeah, and the stat out also would have to go to boiler S/L. So if your S/L on the boiler is live from another source, so the heating. The valve would still be live and hold open.
Every unvented manufacturer will provide a wiring diagram in their instructions for the use of the 3 port mid position valve & the required 2 port that must be installed with it. This is required as under fault conditions there could be an open pathway from the heat source to the cylinder allowing the cylinder temperature to go above 100deg C.
The only exception to this, to my knowledge, is Vaillant who applied & got a dispensation so long as their boiler & cylinders are used together as a package.
Megaflo one below Jon, whats the cylinder?
View attachment 38257