Are you or are you not professionals ? If you wish Plumbing to be a profession and not just some form of labouring then you need to accept that a bit of reading & understanding of technical documents is required for time to time.
Below has been taken free of charge straight off this web site
http://www.planningportal.gov.uk/uploads/br/BR_PDF_AD_G_2015.pdf
3.60 The discharge pipe should not be connected to a soil discharge stack unless it can be demonstrated that the soil discharge stack is capable of safely withstanding temperatures of the water discharged, in which case, it should:
a. contain a mechanical seal, not incorporating a water trap, which allows water into the branch pipe without allowing foul air from the drain to be ventilated through the tundish;
b. be a separate branch pipe with no sanitary appliances connected to it;
c. i
f plastic pipes are used as branch pipes carrying discharge from a safety device, they should be either polybutalene (PB) or cross- linked polyethylene (PE-X) complying with national standards such as Class S of BS 7291-2:2006 or Class S of BS 7291-3:2006 respectively; and
d. be continuously marked with a warning that no sanitary appliances should be connected to the pipe.
Notes:
1. Plastic pipes should be joined and assembled with fittings appropriate to the circumstances in which they are used as set out in BS EN ISO 1043-1:2002 Plastics. Symbols and abbreviated terms. Basic polymers and their special characteristics.
2. Where pipes cannot be connected to the stack it may be possible to route a dedicated pipe alongside or in close proximity to the discharge stack.
A simple search on the tinternet would reveal what polybutalene (PB) or PE-X are if you were unsure.
Sorry if this all sound harsh but come on!!! sick of hearing "no one told me that" go find out.