On a bit of mare of a job, hoping someone on here can give a fresh perspective, cos i'm running out of ideas.
Scenario is as follows. Dentists Surgery over three floors of a converted terrace, approx 12 basins with mixers and 3 w/c's, hot water is via an
unvented cylinder on the top floor.
I was called in to try and sort out why the taps were spitting badly, mainly the hot, but cold as well, problem started in October last year, when Yorkshire Water did some mains work as another shop on the same parade had complained of low pressure.
At first i suspected the strainer in the cylinder multi function was blocked, but no it was ok, also noticed the cylinder did not have a dedicated cold supply, spoke to the manufacturer who confirmed it would be better to have a dedicated cold feed, especially as the cylinder is on the top floor.
Also spoke to Yorkshire Water, even though pressure seems excellent, who confirmed they had tested the supply to the property recently and all is in order, plenty of pressure and flow.
To test the cylinder starving theory i chucked a hose pipe out of the window and connected directly from the stop tap to the unvented, this seemed to cure the hot problem.... happy days!... also took the pipe into the yard and opened the stop tap, water flowed just as you would expect, plenty of pressure and no fluctuations.
Explained my theory to the custard and they agreed to me running a dedicated supply to the cylinder. Couldn't put a price to the job so we agreed a day rate plus gear. Only slight niggle in my mind was why the system had been working ok up to october.
Have spent the last two days running the pipe ( absolute t*at of a job, all welded vinyl floors and nice decor) however we managed to do it with a minimum of mess, also fitted a pressure reducing valve with gauge just after the stop tap, so i could monitor the pressure. bled all the outlets of air, and all seemed rosy in the garden, taps running nicely with no spitting.... nipped off for some late dinner and to do a couple of gas certs. Came back after a couple of hours expecting to stick my bill in, only to find the system full of air again,:yawn: hot and cold outlets both spitting and banging badly for 30 seconds or so before clearing.
Bottom line seems to be that somehow air is being drawn in.....But how and where ? any ideas folks, cos i'm not going to get paid unless i can sort it:bigcry:
TIA
Al.
Scenario is as follows. Dentists Surgery over three floors of a converted terrace, approx 12 basins with mixers and 3 w/c's, hot water is via an
unvented cylinder on the top floor.
I was called in to try and sort out why the taps were spitting badly, mainly the hot, but cold as well, problem started in October last year, when Yorkshire Water did some mains work as another shop on the same parade had complained of low pressure.
At first i suspected the strainer in the cylinder multi function was blocked, but no it was ok, also noticed the cylinder did not have a dedicated cold supply, spoke to the manufacturer who confirmed it would be better to have a dedicated cold feed, especially as the cylinder is on the top floor.
Also spoke to Yorkshire Water, even though pressure seems excellent, who confirmed they had tested the supply to the property recently and all is in order, plenty of pressure and flow.
To test the cylinder starving theory i chucked a hose pipe out of the window and connected directly from the stop tap to the unvented, this seemed to cure the hot problem.... happy days!... also took the pipe into the yard and opened the stop tap, water flowed just as you would expect, plenty of pressure and no fluctuations.
Explained my theory to the custard and they agreed to me running a dedicated supply to the cylinder. Couldn't put a price to the job so we agreed a day rate plus gear. Only slight niggle in my mind was why the system had been working ok up to october.
Have spent the last two days running the pipe ( absolute t*at of a job, all welded vinyl floors and nice decor) however we managed to do it with a minimum of mess, also fitted a pressure reducing valve with gauge just after the stop tap, so i could monitor the pressure. bled all the outlets of air, and all seemed rosy in the garden, taps running nicely with no spitting.... nipped off for some late dinner and to do a couple of gas certs. Came back after a couple of hours expecting to stick my bill in, only to find the system full of air again,:yawn: hot and cold outlets both spitting and banging badly for 30 seconds or so before clearing.
Bottom line seems to be that somehow air is being drawn in.....But how and where ? any ideas folks, cos i'm not going to get paid unless i can sort it:bigcry:
TIA
Al.