A vented cylinder replacing an unvented cylinder, I assume this is a no go as mentioned above, a vented cylinder will not be able to withstand the pressure of mains water. Is this correct?If on the other hand, you just mean that a vented cylinder, with the secondary plumbed in conventionally to an open vent and cylinder feed cistern, is to have its primary coil connected to a sealed primary boiler circuit, then there is nothing wrong with that.