Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
My daughter is.Are you the homeowner?
Whose replaced the parts you?My daughter is.
My daughter is.
No. gas engineer neighbour. He seems puzzled by the noise. He also serviced the boiler about a month ago and was fine then apart from the kettling. Like I say it runs fine other than the resonance vibration for 10secs or so when first starting up. Don't want to throw much more money at it 14 years old now.Whose replaced the parts you?
Thanks for the suggestion. It even makes the noise when he took all the panels off exposing the heat exchanger. Does he need to service it again now that he's replaced the flue collector and heat exchanger? Could the gas mixture have changed?Get the gas engineer to loosen the case mounting hex bolts 1/2 a turn
Great thanks I'll pass that on. Do you have the tb reference that I can give him. I'm tempted to get someone else in to do a service and check the mix.Heat exchanger mounting bolts
Great thanks I'll pass that on. Do you have the tb reference that I can give him. I'm tempted to get someone else in to do a service and check the mix.
Very much appreciated. I've messaged them. Fingers crossed.Sorry I don’t but @king of pipes @ChrisB1982 might
No, I don’t sorry. If not KOP then @EvilDrPorkChop might?Sorry I don’t but @king of pipes @ChrisB1982 might
No sorry I don't either.No, I don’t sorry. If not KOP then @EvilDrPorkChop might?
Boiler now much quieter. Plumber loosened heat exchanger clamps slightly which helped but richening the gas mixture from 8.1% to the specified 9.1% seems to have resolved it many thanks to shauncorbs for his adviceUnable to track down the tb but have had a response from vaillant. The grease is to stop creaking and clicking noise which isn't the problem but the spec for tightening the nuts is only 6nm which I guess he overtightened with the water pump pliers he used. I noticed he also didn't replace the nuts with the new ones supplied with the flue collector. Not sure if that's important enough to get him to change when he loosens them.
Many thanks for your help. I'll post the outcome.
Boiler now much quieter. Plumber loosened heat exchanger clamps slightly which helped but richening the gas mixture from 8.1% to the specified 9.1% co2 seems to have resolved it. Many thanks for your adviceVery much appreciated. I've messaged them. Fingers crossed.
Reply to the thread, titled "Vaillant boiler vibrating cold start" which is posted in Boiler Advice Forum on Plumbers Forums.