H
Homeglow
Hi
I have been to a Vaillant Pro 28 and the symtoms are:
  • Boiler modulating on low in both hot water/heating
  • Coming up with F.75 fault
  • Sounds like air in main heat ex when put into service mode and starts to bang as over heating
I have spoken to Vaillant tech three times now, i have cleaned the low water sensor and the problem is still there. I t sounds like there is air trapped in main heat ex, i have also put the boiler in purge mode three times. I was just seeing if anyone else as had these symptoms, I am going back to change the AAV, low water sensor and the two main flow/return pipes as they are the old type with the rubber connections on and I have been told these can cause blockages. I have also tried to bleed through the pump.
Hi Homeglow.
Possibly a restriction in water flow or pump issue rather than air in boiler/system.
Hi
I have changed a few pumps on the PRO but I can hear alot of water movement on this one, I have thought a blockage after a friend told me the problems associated with the rubber connections on the flow and return pipes. Do you think the blockage could be somewhere else?
When in heating mode can you feel the flow pipe getting hot?
Maybe keep boiler at minimum to avoid 'kettling'
The flow pipe is getting hot and the temp on display ramps up in seconds and then modulates right down to minimum, it only kettles when I put it in service mode. Just a pain in the bum fault, the tech guys said it could be one of 4 faults, its just a shame the parts cost money!
speak to your rep get the new solid pipes replace the water presure sensor check the aav is open . is the boiler in a loft ? put a system cleaner in the system
i have had a simalar fault on a pro 28, if i reset the boiler it was rumbling and banging away the flame was modulating like crazy.turned out to be the reg on the gas meter have you checked inlet gas pressure.