How would you call this?
Doing a safety check, this the only gas appliance and a tenants own cooker.
Working pressure at meter 19.12 mbar. WP at boiler 14.12 mbar. Gas rate good, FGA boiler aswell an readings are fine.
I'd say the carcass, 22mm off meter to bedroom then across to kitchen to boiler 22mm us 18mtrs tops.
I've left it on, everything was working fine. Not effecting the safety of appliance or cooker, but there is a pressure drop.
Advised on fitting a test point under boiler on LGSR.
The boiler has been in for years