hi we have an issue with our heating and water system . new flow switch and new pump , system bled , all done by a professional but still no hot water or heating. when the plumber left yesterday we had boiling radiators and some hot water although the heating was switched off. my suspicion is diverter valve but unsure as to why nothing is working again now. boiler tries to kick in but says FD error (flow)

would be really happy for some advice as we have been 4 weeks without hot water no and the Mrs isn't happy.

thanks in advance
John
 
i tried that lol but they arent answering now or even rang me back. daft as they are local and installed the boiler 4 years ago. looks like weve had a pump for no reason too grrrr
 
Is it an ideal boiler? Which one? It's or a only 4 years old I'd expect it to still be under warranty. If not then perhaps give the manufacturer a call and ask about a fixed price repair.
 
it is an ideal so it must be 5 years as its just out of warranty, i dont think its the boiler as it was working again yesterday but couldnt switch heating side off without turning radiators off.
 
it is an ideal so it must be 5 years as its just out of warranty, i dont think its the boiler as it was working again yesterday but couldnt switch heating side off without turning radiators off.

Sounds like it could be your 3 port valve or even the programmer. Start with everything cold, put a call/demand for hot water and feel your pipe leading to the cylinder on 3 port (should be Port B). Now it probably won’t get hot as you said you don’t have hot water, then feel Port A side (heating) if this is hot then it’s more than likely 3 port being the issue.
 
  • Like
Reactions: Aire
it is an ideal so it must be 5 years as its just out of warranty, i dont think its the boiler as it was working again yesterday but couldnt switch heating side off without turning radiators off.
Yeah I was typing my reply before you mentioned it was a heat only boiler. Why couldn't you switch the heating off? If the system was running when there was no demand, the first place I'd be looking is at the 3 port valve, unless there's a wiring fault, this is the only valve that can overide the controls and fire the boiler up
 
Yeah I was typing my reply before you mentioned it was a heat only boiler. Why couldn't you switch the heating off? If the system was running when there was no demand, the first place I'd be looking is at the 3 port valve, unless there's a wiring fault, this is the only valve that can overide the controls and fire the boiler up

all the controls were off for heating but it was still heating all the radiators. im going to have a quick look this afternoon see if i can see anything obvious especially on the 3 way valve. electrics out of my remit on controls really but these havent been touched other than the new pump being wired.
 
Ok here's where I'm at. Took the front off diverter valve and I can move the shaft left and right. Left motor off to see what happens with flow when I turn the valve. Nothing to the left and nothing to the right but in the middle heating and hot water.
 
Another follow up, water is flowing without the diverter head on and me set the pin to the middle, turned all the rads off to stop the flow around them. It will do temporarily until someone can come round or I'm sure it's diverter valve, thinking I need a complete valve assembly as I'm thinking it's breaking down a bit inside. But I'm not too confident draining the system.
 
Another follow up, water is flowing without the diverter head on and me set the pin to the middle, turned all the rads off to stop the flow around them. It will do temporarily until someone can come round or I'm sure it's diverter valve, thinking I need a complete valve assembly as I'm thinking it's breaking down a bit inside. But I'm not too confident draining the system.

It could be, but you’d be better someone else take a look. I’m surprised no one on here has been in touch.
 
Hopefully the diverter has been put on the correct way arround and wiring to the Clock is ok? With a 3 port Valve the cylinder stat can actually affect how it operates. I've had it where the heating stays on and only water. I'd be having all those checked
 
  • Useful
Reactions: 1 person
Hopefully the diverter has been put on the correct way arround and wiring to the Clock is ok? With a 3 port Valve the cylinder stat can actually affect how it operates. I've had it where the heating stays on and only water. I'd be having all those checked

Thanks
The wiring hasn't been touched, it's original valve and clock so my assumption is it's mechanical but I'm no heating engineer.

Good news is it's kicking in and out this morning still with top on motorised valve. I will clean the magna clean out again today and see how we go.
 
  • Like
Reactions: Burger
Thanks very much, going to try the original plumber as it's his responsibility really but if I have no joy I will message you.

Could anyone please confirm the drain down method, in my mind it's lock off the tank in the loft then turn on hot taps to drain down tank , when that's drained drain the hot water loop from the drain tap at boiler then hey presto should be clear to take off diverter valve.
 
Thanks very much, going to try the original plumber as it's his responsibility really but if I have no joy I will message you.

Could anyone please confirm the drain down method, in my mind it's lock off the tank in the loft then turn on hot taps to drain down tank , when that's drained drain the hot water loop from the drain tap at boiler then hey presto should be clear to take off diverter valve.
No need to drain hot water, your hot water and heating water are seperateted you'll have two tanks in the loft, close off the small one. Turn off power supply to boiler, open drain valve, wait for water to stop, then open bleeds on upstairs rads, wait for water to stop, then open bleeds on downstairs rads. Don't forget to add inhibitor back in the system when filling back up. Also check the condition of the water when you drain down. If it's mucky it might give a clue as to why your system is having issues
 
No need to drain hot water, your hot water and heating water are seperateted you'll have two tanks in the loft, close off the small one. Turn off power supply to boiler, open drain valve, wait for water to stop, then open bleeds on upstairs rads, wait for water to stop, then open bleeds on downstairs rads. Don't forget to add inhibitor back in the system when filling back up. Also check the condition of the water when you drain down. If it's mucky it might give a clue as to why your system is having issues

Thanks very much, got me head confused on the water heating loop lol. I'm happy doing that , I have drained the upstairs rads before do I have to drain the downstairs rads too?
 
Hi, the saga continues, plumber came back and put new diverter valve on, we have come back off holiday and no hot water, pump works diverter valve works , as said before new flow sensor fitted too, only thing I noticed when I cleaned magna clean is metal fragments attached , will try to add a picture. We are going to get a different plumber, could I be right in thinking all the pipes could be caked up in the fragments. We are at a loss now as the best route to follow as if my understanding is correct it's really just a simple flow circuit.
 

Attachments

  • 1980582062_1_27.png
    1980582062_1_27.png
    718.1 KB · Views: 58
And have you checked your 3 port again? If that's coming out of your filter, could be blocking your 3 port 😱
I tried the new 3 port on manual setting and that didn't help, also tried heating and that's not functioning although you can hear the valve motor move. I know is difficult to diagnose on the internet but it's doing is in. If I knew how I could flush it through I would try myself but other than that it's midweek untill we can get a new plumber out. There can't be much else in the system can there. Again I'm guessing but there must be a blockage somewhere. You can hear the water start to flow and you can feel it throughout the pipes to tank but I suppose that could be pump vibration.
 
Nothing is getting hot , boiler won't fire just keeps coming up flow fault. I don't know if the emersion is still connected as I can see wires or where a heating element would be.
 
  • Like
Reactions: Burger
I presume I can wire in a Immersion heater, I'm just trying to find the length I can use. Attached image is my tank info.
 

Attachments

  • IMG_20190803_204529_50.jpg
    IMG_20190803_204529_50.jpg
    390.1 KB · Views: 87
Looking at the shiote in the filter, could be stopping it. Can you take a photo of your pump (if it’s near cylinder) and 3 port layout? Just to maybe get a different perspective.

Best I can get I'm afraid no David bailey
 

Attachments

  • IMG_20190803_210325_50.jpg
    IMG_20190803_210325_50.jpg
    386.7 KB · Views: 93
  • IMG_20190803_210343_50.jpg
    IMG_20190803_210343_50.jpg
    364.2 KB · Views: 82
  • Like
Reactions: Burger
Hard to tell from that photo, but I’m unsure if that first valve on the pump is fully open? Check both are fully open (anti-clockwise). Also check your boiler thermostat is turned up.
 
Are you getting no flow on heating and hot water or just when your calling for hot water?

On both , when it was first so called repaired it all worked on pump speed 2 , but then struggled so had to be moved to 3, my thinking is it's a blockage moving around but I'm doing a lot of thinking over it all probably too much lol.
 
On both , when it was first so called repaired it all worked on pump speed 2 , but then struggled so had to be moved to 3, my thinking is it's a blockage moving around but I'm doing a lot of thinking over it all probably too much lol.
It could easily be an airlock after the repair. The plumber most likely drained down to some degree to change the valve so an air lock would not be uncommon. Try cycling your hot water on and off for a few minutes. Using the programmer turn the hot water on, for 10 - 20 seconds, off for 10 - 20 seconds and do this for a few minutes. You should be able to hear the water move and possible hear bubbles in the system. Other than that it could be a blockage or even a blocked cold feed/dried up f&e tank.
 
  • Like
Reactions: Burger
Sounds like air in the system, try bleeding all radiators and any manual / automatic vent points. If no air comes out I'm afraid you'll have to hire another plumber or get the first one back, I hope you haven't paid him!

I would never leave a customer like this
 
Sounds like air in the system, try bleeding all radiators and any manual / automatic vent points. If no air comes out I'm afraid you'll have to hire another plumber or get the first one back, I hope you haven't paid him!

I would never leave a customer like this

We have paid him as it was working. Albeit was only £240 but it's the time frame.
 
The water was,is dirty. It was a bit caked up but free flowing now, rads have bled and you can tell when the pump kicks in as it increases the pressure of water coming out the rad.
 
Ok am I doing something wrong, this is the tap the plumber drained the water out of the system with above the boiler. In my little mind I thought if I opened that valve/tap water should come out, am I wrong do I have to open anything else. I don't want to completely drain everything down just view the water or make sure it's making it to the boiler and it's not just air pushing around.
 

Attachments

  • IMG_20190804_165017_50.jpg
    IMG_20190804_165017_50.jpg
    262.7 KB · Views: 46
Ok am I doing something wrong, this is the tap the plumber drained the water out of the system with above the boiler. In my little mind I thought if I opened that valve/tap water should come out, am I wrong do I have to open anything else. I don't want to completely drain everything down just view the water or make sure it's making it to the boiler and it's not just air pushing around.

Yes that’s the drain cock and is used for draining purposes.
 
So I should have water come out of that?
Water will come out so long as the washer isn't stuck or the valve blocked. If the plumber recently used it then it should be fine. What I would do is attach a hose, open the valve and then go in the loft to check that the water level in the tank drops and refills. This will prove if the cold feed is blocked or not.
 
  • Like
Reactions: Burger
Water will come out so long as the washer isn't stuck or the valve blocked. If the plumber recently used it then it should be fine. What I would do is attach a hose, open the valve and then go in the loft to check that the water level in the tank drops and refills. This will prove if the cold feed is blocked or not.

Nothing comes out when I undo the square bit, do I have to push or press anything, it opens very easily but not even a drip out of it when square bit fully open.
 
Nothing comes out when I undo the square bit, do I have to push or press anything, it opens very easily but not even a drip out of it when square bit fully open.
If it was me, I'd slightly unscrew the circular nut that the square nut passes through, don't take it all out but it will allow you open the drain valve further, this can sometimes free off the washer in the valve. Be warned though, if the washer is knackered you could find the valve won't re seal. Personally I'd wait till tomorrow till shops are open to get a replacement if needed.
 
  • Like
Reactions: Burger
If it was me, I'd slightly unscrew the circular nut that the square nut passes through, don't take it all out but it will allow you open the drain valve further, this can sometimes free off the washer in the valve. Be warned though, if the washer is knackered you could find the valve won't re seal. Personally I'd wait till tomorrow till shops are open to get a replacement if needed.

I Agree with Craig, best wait til tomorrow 🙂
 
I've given up properly now.

That lock ring thing was quite loose.

My partner said she saw the the plumber draining water out there with hose attached with clear water running through, again in my head the colour of water in header tank how can it be running clear.
 
  • Like
Reactions: Burger
I think it's beyond my knowledge understanding. I can see how it all works but I'm not a plumber and I think it's best left to the professionals, just not the same one we had before.

Thanks again for all the advice.
 
  • Like
Reactions: Burger
Well another 5 hours with a different plumber and guess what, no hot water or heating. I'm at work but the Mrs has said they have replaced a load of pipework in the airing cupboard and got some sludgy water out. But it's still coming up flow error. Going to have to come back another day, dread to think on cost of this little lot. Sad times.
 
  • Winner
Reactions: Burger
Well another 5 hours with a different plumber and guess what, no hot water or heating. I'm at work but the Mrs has said they have replaced a load of pipework in the airing cupboard and got some sludgy water out. But it's still coming up flow error. Going to have to come back another day, dread to think on cost of this little lot. Sad times.
When you get home take a pic of the new pipe work, just to keep us updated.
 
  • Like
Reactions: Burger
I haven't yet no, we got the other plumber to fit the 3 way valve then paid him as it was ok for a couple of days then we went away . The Mrs then called the people that service our boiler yearly and to be fair they turned up as promised, even put a job off to do ours. If it's just a case of flushing the rads with a hose pipe that's something I can do easy enough, had rads off before and fitted new ones so sure I can manage that.
 
  • Like
Reactions: Burger
I think that's what it's looking like. They drained water off as per pic.no real metal bits just sludge and mucky water. Their opinion and that's all it is at the moment is as soon as the pump starts to drawer water it's drawing sludge slowing everything down to a stop.
 

Attachments

  • 15650279055935397636329458110501.jpg
    15650279055935397636329458110501.jpg
    1.4 MB · Views: 49
Tall glass what they fetched off

Small glass what I've just drained out of tap off the top of the boiler pipe
 

Attachments

  • 15650296999754567895464705969238.jpg
    15650296999754567895464705969238.jpg
    1.3 MB · Views: 49
  • 15650297160128048946572465347743.jpg
    15650297160128048946572465347743.jpg
    1.2 MB · Views: 53
A bit more info, when the new Plumber was doing his stuff the water he got to run clear and the hot water started to heat up, he then tried the heating side and that screwed the whole system.water went all crap again and boiler wouldn't fire.
 
That's new pipes, not as many as I thought but new none the less.
They've replaced the cold feed, it's a typical place for the system to block up there. Obviously there's no way of knowing whether it was blocked or not though. I personally wouldn't have installed a iso valve either, I'd have gone with a full bore valve and removed the handle so it can't accidently be turned off.
 
  • Like
Reactions: Brambles and Burger
A bit more info, when the new Plumber was doing his stuff the water he got to run clear and the hot water started to heat up, he then tried the heating side and that screwed the whole system.water went all crap again and boiler wouldn't fire.
Sounds like a good power flush should see you right.
 
  • Like
Reactions: Burger
To me it looks like the pumps are fine it's the fact that the flow and return are joined together that gets me.

But in all honesty I cant really make every thing out as it hurts my eyes. RIP it out and do it again.
 
To me it looks like the pumps are fine it's the fact that the flow and return are joined together that gets me.

But in all honesty I cant really make every thing out as it hurts my eyes. RIP it out and do it again.
It's not required but I thought that was a bypass and that the gate valve would only be partially open.
 
The pump just switches off when the flow message comes up but yes it displays between 29 and 34 watt when running.

OK then, if that is a 6M pump and running on fixed speed 3 @ 30W then it is only circulating ~ 0.2 m3/hr or 3.3 LPM, just turn the rotary knob fully clockwise and then back it off a little, when it starts up adjust it to read 4M (flashing), it will then change to display the power, if, in fact the flow rate is only ~ 3 LPM then it will only read 15/18w, the higher the better, to give any meaningful flow at this setting it should read ~ 25W which is ~ 13/15 LPM.
 
JP

I would be wary of trying to fix this by making ad hoc modifications ( new bits of pipe and valves et al ) and then trying to run the system. You run the possible risk of either making the problem worse or possibly causing expensive damage to the boiler.

Isolate the heating system other than one radiator (preferably the one closest to the boiler ) and then systematically work through the boiler + single rad hydraulic system. At the same time check and test the individual controls against the logic diagram. Also fit a quality magnetic filter on the return to the boiler.

Once you are satisfied that you have a clear hydraulic path on your mini system - configure the pump to run with the boiler off and satisfy yourself you have a good clean flow path.

Thereafter and only when you have a clear hydraulic flow path, get the boiler operational at minimum rate and stable before you systematically look at the rest of the system.

At the end of the day, you have a fairly straightforward system to analyse, approach it in a logical step by step fashion - and make sure that you have not had anyone in to work in this problem who has changed the flow paths.

Always have in mind that you may have more than one problem with the system - hence the need to be systematic, patient and don’t jump to conclusions (sludge is an issue, but in my experience, a serious sludge problem = no flow, not erratic flow which are (to my mind) the symptoms you are describing ).



A suggestion - get the new iso valve by the pump removed - it is not full bore so is restricting flow - it may seem churlish, but the last thing you need at the moment is anything that disrupts or distorts the hydraulic flow

Hope this helps
 
Last edited:
  • Like
Reactions: John.g and Burger
JP

I would be wary of trying to fix this by making ad hoc modifications ( new bits of pipe and valves et al ) and then trying to run the system. You run the possible risk of either making the problem worse or possibly causing expensive damage to the boiler.

Isolate the heating system other than one radiator (preferably the one closest to the boiler ) and then systematically work through the boiler + single rad hydraulic system. At the same time check and test the individual controls against the logic diagram. Also fit a quality magnetic filter on the return to the boiler.

Once you are satisfied that you have a clear hydraulic path on your mini system - configure the pump to run with the boiler off and satisfy yourself you have a good clean flow path.

Thereafter and only when you have a clear hydraulic flow path, get the boiler operational at minimum rate and stable before you systematically look at the rest of the system.

At the end of the day, you have a fairly straightforward system to analyse, approach it in a logical step by step fashion - and make sure that you have not had anyone in to work in this problem who has changed the flow paths.

Always have in mind that you may have more than one problem with the system - hence the need to be systematic, patient and don’t jump to conclusions (sludge is an issue, but in my experience, a serious sludge problem = no flow, not erratic flow which are (to my mind) the symptoms you are describing ).



A suggestion - get the new iso valve by the pump removed - it is not full bore so is restricting flow - it may seem churlish, but the last thing you need at the moment is anything that disrupts or distorts the hydraulic flow

Hope this helps

thanks for that, it is getting a bit to much for me really I can only do very basic stuff. we just need someone to fix it lol , its been nearly 5 weeks now and I have no more hair left to pull out. I have a logical mind but I just cant seen to get my head around this. if we could just get hot water that would be ok for now until the rest can be fixed but its just not going right. in my head yet again ive got set the timer so its just HW which should close the rads off? drain the water out from the tap above boiler until it runs clear and see if the boiler then kicks back in or is that too simple, if that worked for a couple of days or so I could start opening one rad at a time. im getting to a point where im over thinking and clutching at straws I think.
 
JP

I have not seen the system - but it is not complex. At a basic level there is something that is severely restricting flow - I doubt that that is just sludge ( but I am possibly wrong).

From a heat perspective, the issue you appear to have is either at or before the three position valve and the heat exchanger, where the pipework is of a reasonable diameter - but the heat exchanger obviously is not.

I would not keep on trying to fire the boiler until I was satisfied that I had a clear hydraulic path through the boiler - if you do and the overheat sensors fail ( unlikely, but if they are being tested repeatedly!) you could make the current problem worse.

On issues where a number of people have tried to fix it, you sometimes find that with the best will in the world they have changed something that has compounded the problem.

It is unlikely that the people you have had to look at the system are novices, but I think it is likely that you have at least two concurrent problems.

With respect to the people who have “serviced” your boiler - they have not in my view done a proper job - the quality of your system water has not got into that state in a year.

It is generally easier ( in my experience ) to get a system operational from the central heating circuit rather than the hot water side ( it eliminates any potential issues that may be within the tank pipework)
 
  • Like
Reactions: Burger
I haven't changed anything its all been done by "qualified " plumbers.

the boiler was serviced in February if I remember correctly.

Its probably most unlikely but you can easily check that the circ pump is pumping in the right direction by checking the arrow on the pump body, also if you are thinking of doing a few things yourself, if you can run the pump with a separate (elec) supply with boiler powered off and then open that three way valve manually to its various settings you can then play around with venting rads etc and see if that pump power increases (speed 3), it should increase to ~ 38/40 W and you will then know that you are getting a decent flow before firing up the boiler again.
If a decent flow rate cannot be achieved then possibly the boiler Hx is fouled.
 