When is a room air vent for flame effect gas fire really needed (with BS)

View the thread, titled "When is a room air vent for flame effect gas fire really needed (with BS)" which is posted in Air Sourced Heat Pumps Advice Forum on UK Plumbers Forums.

P

PB108

[FONT=&quot]Some history is that one gas engineer ([/FONT]who checked safety after fitting of a new gas meter) in the past said I had to have an air vent fitted in the lounge as gas fire required it, but then another engineer (British Gas) said if it is 7½ bar & below this is not necessary, so blocked the said up again as it just obviously lets cold outside air in.

However another gas engineer doing a 1st annual safety check today, before letting out that old house, failed it as I had blocked up said air vent; he was willing to un-fail it if I could quote for the flame effect gas fire manual states that it doesn't require a nearby air vent or proof of the British Standard bar rate stating similar.

What is the exact legal requirement and quote of the Gas Safe standards anyone please? (not hearsay)
 
Manufacturers instructions are always ( if available ) taken as the correct installation method.

There has been confusion occasionally in the past between what is known as a DFE ( Decorative fuel effect) gas fire and an ILFE ( Inset Live Fuel Effect ) gas fire.

Unless the manufacturers instructions say otherwise a DFE normally needs ventilation, (even if it was 7KW or less). This was due to them being installed in a similar method to an open fire ( solid fuel). The flue/chimney is fully open on these with little or no restriction and therefore the volume of air from the room, which is taken up the flue along with the products of combustion is a lot greater than it is with an ILFE.

Do you know which type yours is ?
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "When is a room air vent for flame effect gas fire really needed (with BS)" which is posted in Air Sourced Heat Pumps Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
PB108,
Last reply from
Last Plumber,
Replies
2
Views
3,452
Back
Top