THE BOILER IS OFF NOW.THANK YOU ALL.#croppie that is what I am thinking about! were they allowed to install it few cm under the window ?and so close to the wall???? Still searching the web...and can not find the answer
 
It was never allowed to be installed like that.

This is what it says in the BS

Where two or more vertical fanned draught chimney configurations
terminate in close proximity at the same height, they shall be separated
by at least 300 mm. Where any one vertical outlet is more than 300 mm
above the other, then they shall be separated by at least 1 500 mm.

Where any vertical fanned draught chimney configuration outlets is
within 2 000 mm measured horizontally of an opening window, then it
shall be at least 300 mm above the opening.
 
Nicko, Vaillant say this with regards to flue positioning (Page 14 of the boiler mi's)

Fluing.JPG
 
So now my question is how it was passing gas inspections?for around 15 years!!!!! Or more??? Who is responsible for such a huge negligence ?
 