Worcester over heat on DHW.
View the thread, titled "Worcester over heat on DHW." which is posted in UK Plumbers Forums on UK Plumbers Forums.
If it was a restriction I would imagine it would happen when the boiler is running on max not so much after it had been running for a while.
My guess would be pump dodgy but I thought I would mention everything else so they can check it all instead of going to the job seeing if its modulating then coming back on here then checking the pump and coming back on here.
Yeah wasn't going against you so much just trying to stop op wondering where to start with all of it lol.
They mentioned they'd checked pump and that was all ok...unless I'm mixing posts up... Quote possible it's Friday night after all 😀
Thanks for everyone's input. Most appreciated.
Yes I did see the pump running when it was doing it, and it couldn't be slowed with a screwdriver, but I suppose there is a chance it may have briefly failed for a second, so I'll test it with a voltage pen to see if it briefly looses power. That would explain the kettling and it shutting down. I'm not sure about the oh stat failing as it was over heating. I'll check gas pressure to see if it's modulating. I was thinking it would be a plate blockage as it only does it on DHW and not in max service mode. Surely the only difference there is the plate heat exchanger being used in DHW mode.
Okay went back to check a few things today,
: Linked out over heat stat and still over heated, linkef out flue over heat stat, still over heated.
: Temps going in and out plate to plate where about 28 degrees different. Got up to 76 in 47 out before it shut down.
: Powe to the pump is constant until it shuts down, then it pulses for a while before the fan comes on and it fires.
: Gas pressure went up and down, but only by 1/2 a mbar so thinks it's modulating. The water flow isn't very high so to me it sounds okay. When the flow is reduced at the tap it does modulate right down.
Surely it can only be the plate to plate do you think??
Surely it can only be the plate to plate do yoy think??
Sounds like plate is OK to me, but could be wrong.
water incoming temp around 15 dc plus the 28 dc rise give you 43 dc hot water temp
normally in hot water mode the boiler wont modulate eg turn tap fully on should stay on max
Sorry so are you saying it sound like the plate needs replacing? Water at the tap was about 53/55. Is it scaled up do you think?
Have you got temp clamps for your analyser can you get them as close to the flow of the heat exchanger as possible. See what temp you have coming out of it.
I would be saying pump or plate. Myself. Whip the plate out and have a look inside.
If water is coming out at that temp doesn't seem much wrong with plate IMO.
Isn't so easy on the Juniors, you have to take the hydraulic block out if I remember correctly. And tbh if you ain't got a new washer pack it's going to leak.
Can get the plates out on them if you cut the hot water outlet pipe. You can then wiggle it out the back down that gap (provided you've got clearance below the boiler to do it).
Though still would of gone the f5 trick personally to do a mini clean on it first.
And obviously check the vanes on the pump too to check no debris in there.
Don't see much else that can be suggested to be honest.
If thermistors are in range, pump voltage is constant when on demand, Ch runs fine, boiler modulates down etc, pump confirmed to not be cutting out etc then there's little else that can cause it.
But without checking and confirming all the above then it'll still be guesswork.
The only thing that puts me off doing the f3 trick is that wouldn't work on the water side. So if that's scaled up the only thing I could do would be replace it. And yes I've changed a few by cutting a pipe and squeezing it out. I'm always reluctant to replace anything with out being fairly positive it'll sort it, I do hate these kind of faults!
Whilst I've had plenty of scaled plates causing poor hot water performance I've never had scale on the dhw side causing boiler overheating, as the system side would be clear and modulate down based on flow and return thermistors.
Just my experience though.
I have had them before when the plate to plate is really scaled up and it makes all sorts of kettling noises with the boiler shutting down. It's not like that though with this one. Still not sure what to do next.
On hot water mode the modulation is carried out by the dhw thermistor. The primary thermistors are basically high limit stats and should cut the boiler out before it over heats.
Sorry I disagree.
The best route for the customer is to diagnose and fix it yourself.
All the manufacturers care about Worcester especially is selling boilers they re not worried about the customers or the installers.
Reply to the thread, titled "Worcester over heat on DHW." which is posted in UK Plumbers Forums on Plumbers Forums.
billski,
billski,
