Hi all...got some issues....drained my working ok system yesterday to upgrade some 15 to 22 on the flow and return rad circuit.
Refilled and bled up.
Fired boiler up, had hot water and rads for 3-4 hours...
Turned off to cool.
Boiler would not fire on timer later, demand wouldnt work either....
Noticed that the pump when working did sound like it was passing bubbles...if that makes sense...?
Also, boiler temp was very high, and heat exchanger was boiling hot to touch.
This morning no hot water or heating on timer fired boiler, so i switched both to demand, i think the boiler woke up, but temp went from 30s to 102 in a couple of minutes.....

Last night i cracked the bleed nipple at the bottom of the heat exchanger and there was water present.

Im assuming i have air locked boiler?

I never had any problems like this with the gravity fed system....
 
99% sure it will be air

Check to ensure heat exchanger is vented, system filter too (I've had systems where nearly all air is caught in the filter and it takes ages to keep bleeding it waiting and then repeat). Once everything is vented properly then you need to start getting some flow moving and the pump will soon clear the air. Start with your hot water only.

If your boiler isn't firing still and it sounds like the pump is cavitating then unplug the connector for a second or 2 or hold the switch between 2 different speeds to stall it, this will let the air escape and allow the pump to keep trying to clear the air.

If you have no luck with the hot water (I had one this week) then run the heating only and shut down every radiator but one, if you have a Y plan make sure you turn your cyl stat down to ensure the valve shuts the hot water. Then go round once and turn a new rad on and the old one off each time they get hot, then finally introduce the hot water.

A photo of your pump and pipe work in the airing cupboard may help too
 
Yep air locked try running on hot water only if you have a cylinder
 
99% sure it will be air

Check to ensure heat exchanger is vented, system filter too (I've had systems where nearly all air is caught in the filter and it takes ages to keep bleeding it waiting and then repeat). Once everything is vented properly then you need to start getting some flow moving and the pump will soon clear the air. Start with your hot water only.

If your boiler isn't firing still and it sounds like the pump is cavitating then unplug the connector for a second or 2 or hold the switch between 2 different speeds to stall it, this will let the air escape and allow the pump to keep trying to clear the air.

If you have no luck with the hot water (I had one this week) then run the heating only and shut down every radiator but one, if you have a Y plan make sure you turn your cyl stat down to ensure the valve shuts the hot water. Then go round once and turn a new rad on and the old one off each time they get hot, then finally introduce the hot water.

A photo of your pump and pipe work in the airing cupboard may help too
OK...heat exchanger vented as in....?
 
99% sure it will be air

Check to ensure heat exchanger is vented, system filter too (I've had systems where nearly all air is caught in the filter and it takes ages to keep bleeding it waiting and then repeat). Once everything is vented properly then you need to start getting some flow moving and the pump will soon clear the air. Start with your hot water only.

If your boiler isn't firing still and it sounds like the pump is cavitating then unplug the connector for a second or 2 or hold the switch between 2 different speeds to stall it, this will let the air escape and allow the pump to keep trying to clear the air.

If you have no luck with the hot water (I had one this week) then run the heating only and shut down every radiator but one, if you have a Y plan make sure you turn your cyl stat down to ensure the valve shuts the hot water. Then go round once and turn a new rad on and the old one off each time they get hot, then finally introduce the hot water.

A photo of your pump and pipe work in the airing cupboard may help too
Il put a pic up
 
Valve and pump arrangement
 

Attachments

  • 20230316_172407.jpg
    20230316_172407.jpg
    553.8 KB · Views: 12
Right so its not open vented.

Typically sealed systems are incredibly easy to get air locks out of.

Just to be sure, that's an old photo right? As your pump and valves aren't wired in.

Need a photo above the boiler of pipework arrangement too and one inside to tell you where to vent the heat exchanger, surprised though with a sealed system the pump won't clear that.

Check what speed your pump is set too and then turn it down to 1 which is the slowest, this may help prevent cavitation until the air clears
 
Right so its not open vented.

Typically sealed systems are incredibly easy to get air locks out of.

Just to be sure, that's an old photo right? As your pump and valves aren't wired in.

Need a photo above the boiler of pipework arrangement too and one inside to tell you where to vent the heat exchanger, surprised though with a sealed system the pump won't clear that.

Check what speed your pump is set too and then turn it down to 1 which is the slowest, this may help prevent cavitation until the air clears
 

Attachments

  • 20230325_171104.jpg
    20230325_171104.jpg
    429.9 KB · Views: 10
Try this. No guarantee that it will work but you have few options. Completely lose the bottom pump valve. Slowly loosen the top pump valve's compression nut, water / air will bleed out and may be enough to release the air lock.
 
Close all but one rad closest to the boiler upstairs turn ch on and ramp the pump upto 3 if it’s not already on it and let it run
 
Leave it don’t reset if pump is running
Pump had stopped, started after reset. Did this twice, then had f11, did another reset, opened the drain on the heating return and seemed to get air out, or at least water that was very oxygenated....?
Left it 30 mins got heat at the one rad with no valves that i left on, bled this and had loads of air, gradually bringing one rad back on at a time and bleeding out...
Swems to be going in the right direction....
 
Pumps controlled via boiler so yes keep resetting if faulting out once one rad gets hot and you’ve bled it a few times and topped the pressure back up if dropped open another rad and leave the good one as is etc

Will take time but should shift
 
Pumps controlled via boiler so yes keep resetting if faulting out once one rad gets hot and you’ve bled it a few times and topped the pressure back up if dropped open another rad and leave the good one as is etc

Will take time but should shift
Is the general oppinion that the system has been plumbed up wrong, ie. It needs a bleed of, or is it just some do, some dont secnario....?
 
Is the general oppinion that the system has been plumbed up wrong, ie. It needs a bleed of, or is it just some do, some dont secnario....?

It’s good practice to put air vents in if the boiler is above the pipework eg drops down
 
You can see from the diagram below anywhere the pipework goes upwards it should have an air vent (marked with an X). Radiators are massive catchments for air with an air vent. In theory

In the real world you can get over small high spots (such as floors being out of level), specially on a sealed system as its easier to clear. I'm one for never ever putting one in but I've seen tons of systems where some plumbers don't care

The second photo shows a system where no additional air vents are needed
 

Attachments

  • 1679775852995.png
    1679775852995.png
    8.3 KB · Views: 10
  • 1679776178709.png
    1679776178709.png
    3.7 KB · Views: 8
You can see from the diagram below anywhere the pipework goes upwards it should have an air vent (marked with an X). Radiators are massive catchments for air with an air vent. In theory

In the real world you can get over small high spots (such as floors being out of level), specially on a sealed system as its easier to clear. I'm one for never ever putting one in but I've seen tons of systems where some plumbers don't care

The second photo shows a system where no additional air vents are needed
Ah right interesting....
So a need for a vent before i settle up....?
 

Reply to Boiler issues not firing after refill in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
123
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
442
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock