dom brennan

Plumbers Arms member
Plumber
Gas Engineer
Messages
234
hi i was just wondering if this is normal or it it was a mistake. the F+E tank never had a vent on it, we drained it down and it took 2 hours to get up and running. some of the air was coming though the cold feed to the primaries to the tank. I've had a look though my college books but can't find anything. thanks dom
 
22mm cold feed off the tank? Combined feed and vent. Bit unusual but allowed on certain boilers.
 
i don't really know much about this kind of things but if the pressure got to much it would usually go back into the F+E tank, so does it go into the Cold water storage cistern but wouldn't that contaminated the hot water
 
F&E is heating (primary)

Cold water storage is supplying your domestic hot water, via the cylinder, and cold tank fed outlets.

I assume the tank you are talking about is the f&e (smaller of the two tanks).
 
but the primary is the same water in the radiators so if that pressure got to high for some reason i would go into the cold water storage or would this never happen i tried asking my employer but he just said he doesn't know
 
No Dom when the heating gets warmer it expands back into the f&e tank back through the feed pipe.
 
Like Ted say's....the primary water in the rads will expand back into the the feed and expansion tank (smaller one) and isn't connected to the cold water storage tank (big one). So no chance of contamination.

Primatic cylinder is another thing to go into, but I don't come across very many.
 
Also, your employer probably does know, but is too busy to explain it, which is common. Hence why this forum is helpful.
 
Status
Not open for further replies.

Reply to F+E tank with no vent in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi so I changed a towel radiator in bathroom from a normal radiator. I bunged the f&e tank and vent pipe , drained about a pint of water out the...
Replies
3
Views
611
    • Like
Hi I recently did some pipe insulating in my loft. The only two I didn't do were the vent pipes. Not sure if that is the right term for them...
Replies
2
Views
376
J
Moved into an old house that has a vented gravity fed system (cold water tank and feed + expansion tank in the attic). I need to replace all...
Replies
4
Views
734
Hi all, Got a nightmare situation with a central heating system I recently adopted. It's an open vent system with a combined F&E pipe, with a...
Replies
17
Views
2K
I recently took off an end stop on the vent/expansion pipe over the heating header tank. I now know why it was capped off. When the 2 way valve...
Replies
15
Views
2K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock