I have recently had Honeywell Evohome controls installed. Since this was done I have had loud noises coming from the radiators and pipes at random times. I have just had one radiator changed and I now have a MUCH louder noise but at least I can now create the conditions to cause it to happen.

The heating system is a Worcester Bosch Greenstar 30 CDI System. The property is a bungalow with the boiler in the garage. There is a hot water storage cylinder in the garage which has a zone control valve connected to the Honeywell system.

There is no longer any zone control valve on the radiators relying on the Honeywell valves to control the water flow. There are 12 Honeywell valves. The pipes initially go down from the boiler and then up into the garage ceiling. There is an automatic bypass between the flow and return. The pipes run from the garage into the bungalow ceiling and then down through an airing cupboard into the solid floor and then are distributed to the radiators. There is a separate pair of pipes that feed the bathroom towel rails. These have never had a zone valve but the other radiators did originally have a zone valve controlled by the CH thermostat.

The system was drained down to fit new TRVs to 4 radiators when the Evohome was installed. The remaining TRV bodies were reused. Since then we have random loud vibrations from the pipework. this was mainly the return pipe that was vibrating.

In preparation for having the kitchen refitted I have just had the kitchen radiator (last Friday) replaced with a narrow/tall one and moved about 40 cm sideways. The original TRV body was re-used but moved to the return side rather than the flow side. The system was partially drained to change the radiator. Initially no water was flowing and the installer had to close all the other radiators off to force the water to flow to the new radiator.

I now have the new radiator working properly BUT when the Evohome starts to shut down the radiator (having reached the set temperature) there is a VERY loud noise coming from the radiator and pipework. the pipes in the airing cupboard are vibrating quite violently. The same thing happens when it is opening up again. The vibration can be started and stopped by slightly adjusting the TRV. I think this mainly happens when most of the other TRVs are closed and the kitchen one is only partly open. I assume that the boiler flow is running through the automatic bypass.

I have bled all the radiators and looked at the automatic air vents in the loft on the flow and return pipes. One released some air.

Can any of you make any suggestions. I have tried to get the heating engineers to come up with a fix but they have not responded to my request so far.

IMG_20180302_152227.jpg


IMG_20180306_185448.jpg


IMG_20180306_185603.jpg
 
Honetwell valves ar best fitted to the flow. They can make a banging sound when turning off.
Also when those valves,were installed, an automatic bypass valve should have been fitted.
 
After looking at your pic. You do have a bypass valve.
So it’s probably valves fitted on the return.
 
The vibration usually goes on for several minutes. I have stopped it by adjusting the valve after more than 5 minutes of continuous noise.
 
I have found a diagnostic status report on the Honeywell Evohome controller which might help someone to shed some light on my problem. If I have understood the display correctly it shows how far each valve is open. On all radiators, apart from the kitchen one, if the percentage is low some water flows and this seems to increase as the percentage rises (judging by hand and estimating the difference between flow and return temperatures).

The kitchen radiator however behaves differently. There is no flow if the percentage is below around 25% to 30%. If I turn the dial, both flow and return pipes start to get hot, and then the vibration starts. If I turn it up a bit more (3-4 clicks) the percentage displayed changes to 100% and the vibration stops.

Is this a red herring or does this help to pinpoint where I have a problem?

Note that the TRV body is not new and it is not a Honeywell one - it was moved from the previous radiator but was transferred from the flow to the return to assist with the kitchen layout. I have other radiators that are behaving correctly, with the same TRV bodies, with the TRV on the return. The hall radiator for example.

IMG_20180307_180925.jpg
 
Further update:

I have now removed the Honeywell actuator from the TRV body and used manual control to adjust the flow. Moving the manual control from closed towards open I can start the loud vibration and continuing to open the valve it stops again. The movement on the manual control ring is about 1/8 turn.

I then tried all of the other TRVs on the heating circuit and found one other that created a noise. The others would silently move from fully closed to fully open.

I have a videos of the behaviour but I do not appear to be able to upload them. I have included Dropbox links. I hope these can be opened. The first is the bedroom radiator and the noise is at a lower level. The second is the kitchen one and is very loud

Dropbox - VID_20180310_114550_mpeg4.mp4

Dropbox - VID_20180310_114711_mpeg4_001.mp4
 
The bedroom radiator that is also making a noise and causing the pipes to vibrate is already on the flow side.

I have at least one other radiator where the TRV is on the return and that is working silently.

I will discuss this further with my heating installer.
 
Some TRVs are designed to fit on either flow or return indifferently. Others are designed ONLY to work on the flow and will not function properly when on the return, and a third type can be fitted to either but there's a collar you have to rotate depending on which way the water is flowing.
 
There was a vibration from the heating system before the kitchen radiator was changed. I believe the heating engineer probably reused the TRV body and moved it to the return rather than the flow. This was to allow more options for the new kitchen layout.
 
Status
Not open for further replies.

Reply to Loud vibration from Radiator in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I am trying to workout in what order my radiators heat up in order to then balance them. I am able to figure out which radiator pipe is the...
Replies
1
Views
345
Hello, I have a customer with a modern anthracite vertical radiator and a modern TRV and lockshield. The radiator makes a loud metallic bang from...
Replies
1
Views
339
Hi All, I need to replace a radiator in the kitchen, the 10mm copper has split so using this opertunaty to replace it with a towel one and also...
Replies
3
Views
389
Hi, Sorry if question already answered in previous posts, but I can't find a solution to the below: We recently moved house to a new home that...
Replies
7
Views
510
I have a problem with noise and vibrations from my shower when i first turn it on. The problem lasts for about 30 seconds after the shower is...
Replies
0
Views
330
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock