Glowworm Ultimate 50FF + 2x Danfoss HPA2 valves for CH and HW.
Pressurised system. No frost stat and wiring (S-plan – I think) has been OKd by two separate engineers.

At the end of the day, the pump is not switching off when boiler/CH/HW shut down.
After the 6-7 minute pump overrun, the levers on the HPA2 are in the closed position but the pump remains on for hours. This tends to happen more when the whole system is hot and has been running all day.

If I switch off the pump via mains power at bedtime, and switch it back on in the morning the pump comes on even though the boiler cabinet is cold and the controller (Honeywell ST699) is not calling for heat. The boiler fires up when I switch the CH on.

If I then let the boiler run for about 1 minute – or an hour, and then switch off the CH, the boiler shuts down, the pump overrun occurs and the pump stops as normal.

The boiler ia 20 years old, has had several HPA2s and 3 (4?) PCBs. It had a new stat and PCB two years ago and a new top fan a month ago.

Could my problem be a faulty micro-switch on the CH (or HW) motorized valve after a prolonged period of heating or – as has been suggested - a faulty relay on the PCB? (but there are no noises coming from the control box). Or something else?

Any advice would be much appreciated
 
Is your pump controlled by your boiler or is it directly wired into the control wiring centre. If it's your boiler there could be an internal problem with that. If it's into the wiring centre you need to test your switch lives from your control valves to see if either of them are calling when they are off. Hard to say definitively without seeing it in the flesh. So many options to go wrong.
 
Contributing as a spark ....... I would doubt its the valve as this should send the signal to run the boiler .............. not just to the pump to run

Is the pump internal or external to the boiler?
 
Thanks for these two replies. Not sure of answer to 'is pump wired to control centre of boiler'. Looking at the wiring diagram in the Glowworm manual, the pump live is connected to one end of a fuse on the PCB so I possibly need to test the switch lives. Wouldn't harm to check this anyway.
 
Thanks Murdoch - pump is external to boiler. Pretty sure its just the pump that runs and not the boiler as well.
 
Thanks Murdoch - pump is external to boiler. Pretty sure its just the pump that runs and not the boiler as well.

Where is the pump wiring going to / from? The boiler or wiring centre?

What test equipment do you have?
 
If the boiler is controlling the pump then it's going to be something internal to the boiler that's telling it to run so your going to need to get yourself a gas safe engineer.
 
Had several from experience it's the pcb otherwise the boiler would fire up It's a motorised valve
 
Contributing as a spark ... I would doubt its the valve as this should send the signal to run the boiler ... not just to the pump to run

Is the pump internal or external to the boiler?
pump external but overrun controlled by pcb
 
Where is the pump wiring going to / from? The boiler or wiring centre?

What test equipment do you have?

Wiring.JPG
 
You won’t get the answer you’re looking for as we will not give advice potentially leading to diy gas work. Please see forum rules
 