Its interesting that (if i am looking at the right manual) the boiler HX itself requires a head of 5.2M to flow 1.4m3/hr and they specified a grundfos 15/58 pump which even with a NO loss header will only flow 0.7m3/hr @ 5.2m, the UPS2 15-30 60 will flow ~ 1.0m3/hr @ 5.2M so even if you had two of these pumps installed as you suggested in your post #6 you couldn't achieve 1.4m3/hr on the primary side. The spec seems a bit strange?.
You should certainly be OK though with the UPS 8M as you can still go up two settings more (if required) if you eventually opt for PP operation.
Didn't read the attachment properly, they actually DO specify a UPS 15-78 pump further down which makes sense now.
You should certainly be OK though with the UPS 8M as you can still go up two settings more (if required) if you eventually opt for PP operation.
Didn't read the attachment properly, they actually DO specify a UPS 15-78 pump further down which makes sense now.