Hi

(System is header tank in loft, indirect hot water tank)

After the hot water isolation valve under my bath, there is a non return valve between the isolation valve and the hot water tap.

When I switch the hot water (mixer tap) on in the bath nothing happens until I flick the SINK mixer tap on and off and then the hot water runs in the bath (the non return valve sticks closed, till you mess with the sink mixer tap).

I have tried without a non return valve in the line but then water comes out of the overflow from the header tank in the loft, to the outside, so I have put a new non return valve back in.

Now the sink 'trick' doesn't work any more N.R Valve must me stuck closed and won't release. Clearly the N.R valve shouldn't be there.

Any ideas anyone?

Regards
Adam
 
Oh Have you any suggestions for my problem?
Seperate hot and cold taps or a mixer that only allows the mix after the valves, the normal advice for your type of tap and water system would be to fit an NRV, if the pressure is too low to operate the NRV then new taps - unless you want to get a pump installed, but the expense and future maintenance is more costly/problematic than just getting new taps.
 
Sounds like you need new mixer tap, the cartridge has bust and it’s sending cold water up the hot pipe back filling the cylinder then up the expansion pipe, filling loft tank then out of the over flow.
Some idiot has tried a cheap fix by fitting a non return on the hot but the, pressure on the cold is greater and keeping it shut until you open the other tap.

New taps and bin the nrv 😉


Seen it loads
 
Well depends if the taps at fault can you remove the hot side cartridge

This is the tap (photo’s). I can remove it, what do you think?

image.jpg


image.jpg
 
You actually do need NRV's on both the hot and cold pipes as per water regs, one to stop the cold forcing its way up the hot water pipes and filling the header tank up and the other on the cold feed pipe for backflow prevention and possible cross contamination of the potable water. If you are having problems then fit a pressure reducing valve on the cold feed pipe to the tap in question to balance the feeds.
 
You actually do need NRV's on both the hot and cold pipes as per water regs, one to stop the cold forcing its way up the hot water pipes and filling the header tank up and the other on the cold feed pipe for backflow prevention and possible cross contamination of the potable water. If you are having problems then fit a pressure reducing valve on the cold feed pipe to the tap in question to balance the feeds.

Water regs would say you would need one on the cold feed as it cat 2? I think.
 
The problem is cheap taps can't cope with the pressure difference so as someone else has said if you do change the taps you need one that mixes outside of the spout.

Otherwise re pipe your cold feed and remove the non return valve.
 