Any ideas if I might be missing something? Worcester Greenstar 28i junior, hot water runs for 5 to 10mins then boiler flame cuts out and it over heats. I can hear the main heat exchanger kettling and banging for a few mins, boiler tries to fire 3 or 4 times, then it fires up and hot water runs again for 5 or so mins. Boiler is about 8 years old, cpa all good, fan test point -5.5 mbar, central heating water all seems clear, runs fine on max test mode, pump seems strong. Can it only be the plate heat exchanger and the main heat exchanger blocked or possibly some thing else? Cheers.
 
I don't think it's been well maintained as the condense trap needed a good clean out. Would a stepper motor fault cause the boile to kettle and over heat??

Probably not thinking about it, it was more the 52 degrees, just re-read post.
 
If you get constant HW at 52oc and boiler works fine for 5 minutes then Plate HEX isn't blocked, does it modulate correctly when it's on HW?

If it was diverter it would go down CH flow so wouldn't kettle.

Pump would be my bet, check to see if it's getting a Live when it kettles. If it is see if it's spinning/operating when it does the issue. Had exactly same issues on a Baxi/Vaillant where CH seemingly worked fine but HW played up. Baxi pump kept cutting out, Vaillant wasn't pumping it round plate quick enough.
 
If you get constant HW at 52oc and boiler works fine for 5 minutes then Plate HEX isn't blocked, does it modulate correctly when it's on HW?

If it was diverter it would go down CH flow so wouldn't kettle.

Pump would be my bet, check to see if it's getting a Live when it kettles. If it is see if it's spinning/operating when it does the issue. Had exactly same issues on a Baxi/Vaillant where CH seemingly worked fine but HW played up. Baxi pump kept cutting out, Vaillant wasn't pumping it round plate quick enough.
 
Inject some f5 or f3 into the boiler through the bleed point (isolating the ch system isolation valves on boiler) and run the hot water tap for 20 mins to half hour. Will give a good clean out of plate and main heat exchanger and will likely solve it.

Normally would put the temp clamps/probes across plate inlet and outlet as has already been suggested above first though. And a non either some probes from multimeter or non contact voltage detector on the lead to the pump to confirm power supply is consistent to pump.
 
Inject some f5 or f3 into the boiler through the bleed point (isolating the ch system isolation valves on boiler) and run the hot water tap for 20 mins to half hour. Will give a good clean out of plate and main heat exchanger and will likely solve it.

Normally would put the temp clamps/probes across plate inlet and outlet as has already been suggested above first though. And a non either some probes from multimeter or non contact voltage detector on the lead to the pump to confirm power supply is consistent to pump.

That sounds promising.
Have you done that your self with the f3/f5 cleaner?
 
Is the boiler modulating? Keep an eye on the inlet pressure see if it goes up and down.

Remove the motor from the DV and run it round the heating for a bit.

Undo the screw on the pump stick a screwdriver in it if you can stop it pump is shot if it tries to break your screwdriver end off it's all good.

Get it hot and then link out the flue O/H stat.
 
Is the boiler modulating? Keep an eye on the inlet pressure see if it goes up and down.

Remove the motor from the DV and run it round the heating for a bit.

Undo the screw on the pump stick a screwdriver in it if you can stop it pump is shot if it tries to break your screwdriver end off it's all good.

Get it hot and then link out the flue O/H stat.
Okay so if it's not modulating what would cause that and you say link out the o/h stat, why?
 
Okay so if it's not modulating what would cause that and you say link out the o/h stat, why?
Can be dhw temp sensor, PCB or fan PCB that can cause it not to modulate. Would need to find out from manufacturers expected resistance range of thermistor to temperature relation & to find out expected voltages to fan
 
Okay so if it's not modulating what would cause that and you say link out the o/h stat, why?

If it's not modulating then I'd look at thermistor. Generally pcbs on Worcester are not that bad the fans are shocking but if they go they go properly.

Disconnect the FLUE o/h stat. I believe it is linked on the same as the o/h and aps. I've had a couple fail in the past when they start to get hot. They can be tricky to diagnose as they are intermittent.
 
From your description I'm still of the opinion that it's gonna be restrictions causing the issue. As if it wasn't modulating then the hot water wouldn't likely remain at 52degrees.

And flue o/heat stat wouldn't cause it to bang and crash like you've described.

I'd check the thermistor ranges anyway and then do the old f3/f5 trick.
 
From your description I'm still of the opinion that it's gonna be restrictions causing the issue. As if it wasn't modulating then the hot water wouldn't likely remain at 52degrees.

And flue o/heat stat wouldn't cause it to bang and crash like you've described.

I'd check the thermistor ranges anyway and then do the old f3/f5 trick.

If it was a restriction I would imagine it would happen when the boiler is running on max not so much after it had been running for a while.

My guess would be pump dodgy but I thought I would mention everything else so they can check it all instead of going to the job seeing if its modulating then coming back on here then checking the pump and coming back on here.
 
If it was a restriction I would imagine it would happen when the boiler is running on max not so much after it had been running for a while.

My guess would be pump dodgy but I thought I would mention everything else so they can check it all instead of going to the job seeing if its modulating then coming back on here then checking the pump and coming back on here.

Yeah wasn't going against you so much just trying to stop op wondering where to start with all of it lol.

They mentioned they'd checked pump and that was all ok...unless I'm mixing posts up... Quote possible it's Friday night after all 😀
 
Thanks for everyone's input. Most appreciated.
Yes I did see the pump running when it was doing it, and it couldn't be slowed with a screwdriver, but I suppose there is a chance it may have briefly failed for a second, so I'll test it with a voltage pen to see if it briefly looses power. That would explain the kettling and it shutting down. I'm not sure about the oh stat failing as it was over heating. I'll check gas pressure to see if it's modulating. I was thinking it would be a plate blockage as it only does it on DHW and not in max service mode. Surely the only difference there is the plate heat exchanger being used in DHW mode.
 
Okay went back to check a few things today,
: Linked out over heat stat and still over heated, linkef out flue over heat stat, still over heated.
: Temps going in and out plate to plate where about 28 degrees different. Got up to 76 in 47 out before it shut down.
: Powe to the pump is constant until it shuts down, then it pulses for a while before the fan comes on and it fires.
: Gas pressure went up and down, but only by 1/2 a mbar so thinks it's modulating. The water flow isn't very high so to me it sounds okay. When the flow is reduced at the tap it does modulate right down.
Surely it can only be the plate to plate do you think??
 
Last edited:
Okay went back to check a few things today,
: Linked out over heat stat and still over heated, linkef out flue over heat stat, still over heated.
: Temps going in and out plate to plate where about 28 degrees different. Got up to 76 in 47 out before it shut down.
: Powe to the pump is constant until it shuts down, then it pulses for a while before the fan comes on and it fires.
: Gas pressure went up and down, but only by 1/2 a mbar so thinks it's modulating. The water flow isn't very high so to me it sounds okay. When the flow is reduced at the tap it does modulate right down.
Surely it can only be the plate to plate do yoy think??
Sounds like plate is OK to me, but could be wrong.
 
water incoming temp around 15 dc plus the 28 dc rise give you 43 dc hot water temp

normally in hot water mode the boiler wont modulate eg turn tap fully on should stay on max
 
water incoming temp around 15 dc plus the 28 dc rise give you 43 dc hot water temp

normally in hot water mode the boiler wont modulate eg turn tap fully on should stay on max
Sorry so are you saying it sound like the plate needs replacing? Water at the tap was about 53/55. Is it scaled up do you think?
 
Have you got temp clamps for your analyser can you get them as close to the flow of the heat exchanger as possible. See what temp you have coming out of it.

I would be saying pump or plate. Myself. Whip the plate out and have a look inside.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Worcester over heat on DHW." which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
billski,
Last reply from
billski,
Replies
97
Views
3,601
Back
Top