So if it's heating up the room at a rate of between 2.5C - 3.0C / hour, this is too slow? I think it's too slow, but wondering what opinions are.
This is with heating system at ~60C at the boiler, and the thermostatic valve radiator turned up full.
Having used several online calculators the highest BTU I get on any calculator is 3788 BTU using: Radiator Sizing Calculator - BTU and KW - http://www.radcalcer.co.uk/ for the room.rad sounds undersized
It's a WB Combi 30i boiler with the rad below:You say you have a flow temperature of 60°c? Is this a condensing boiler.
I have pointed a contact free thermometer pointed very close to the rad and it gives a temp of ~58 C.From -10 to 21dc 14 mins so something isn’t right
does the rad get hot hot eg 60dc ish
I have pointed a contact free thermometer pointed very close to the rad and it gives a temp of ~58 C.
Thanks.I would say the specs that the manufacturer has claimed are over zealous and would estimate it to emit around 1.5-1.8 kw (max)as it’s basically a single panel rad
Unfortunately I don't have a plumbing background, so I'm unsure what exactly this means.
I understand that k2 is a type of rad. Do you mean if using a double panel 1.2m x 600mm K2 rad this would give an average BTU output of 7401 BTU?
The current rad type which I have would probably need to be a lot bigger to heat up the room in 30 minutes since it's heating the room at ~ 2.5C - 3.0C / hour.
So essentially if I wanted to get this make/model of rad to heat the room up in a reasonable amount of time (and I only wanted one rad as it's a small room) the rad may need to be in the region of twice the output size of the one currently installed?correct
or another rad installed in the same room eg two rads
Also because you are running with a boiler temp of 60C then you will only be getting ~ 65% of a 50 deg rad output or ~ 4810 BTU (1.4kw).So essentially if I wanted to get this make/model of rad to heat the room up in a reasonable amount of time (and I only wanted one rad as it's a small room) the rad may need to be in the region of twice the output size of the one currently installed?
Should the boiler temp be run at a different temperature? I've set the WB combi to the recommended "e" setting and this is usually about 60C.Also because you are running with a boiler temp of 60C then you will only be getting ~ 65% of a 50 deg rad output or ~ 4810 BTU (1.4kw).
If you increased the boiler temp to 75C and with a radiator deltaT of 15C, you would then almost have a 50 deg (47.5) rad again or 94%% output but the boiler is then running with a return temp of 60C which is very uneconomic, if you run with a delta T of 20c you are down to 87% output, all rads should really IMO be oversized by a factor of at least 1.5 to allow for condensing boilers which run most efficiently with return temperatures of 50C or less.It looks like their only larger rad of this style is:
which has 9163 BTU as opposed to the 8218 BTU for the one which I have. I'd guess this won't make a huge difference in getting the room warmed in 30 minutes, so perhaps I might look at some other radiator design.![]()
1800 x 560mm White Vertical Traditional 3 Column Radiator
Create an old fashioned traditional look with these vertical column radiators, 1800 x 560mm and triple layered for extra warmth.www.radiatoroutlet.co.uk
Should the boiler temp be run at a different temperature? I've set the WB combi to the recommended "e" setting and this is usually about 60C.
It looks like their only larger rad of this style is:
which has 9163 BTU as opposed to the 8218 BTU for the one which I have. I'd guess this won't make a huge difference in getting the room warmed in 30 minutes, so perhaps I might look at some other radiator design.![]()
1800 x 560mm White Vertical Traditional 3 Column Radiator
Create an old fashioned traditional look with these vertical column radiators, 1800 x 560mm and triple layered for extra warmth.www.radiatoroutlet.co.uk
Should the boiler temp be run at a different temperature? I've set the WB combi to the recommended "e" setting and this is usually about 60C.