discharge pressure doesn't move except building use. The green eye is not turning, the motor is not turning. Setpoint is 90psi discharge pressure is around 65psi.Discharge / pressure/ flow ?
Discharge pressure is in discharge line, reading outlet pressure continuously. It is the controlled parameter. This pump will run in manual at a set speed. but when switched to normal it just stops. We are beginning to think there is an issue with the electronics in the controller itself since nothing we can do will make it run in auto (normal) to control, pressure. Unless we are missing something, which is one reason I am here. Several Grundfos techs have looked at it to no avail. My next step is to rip the vfd and control out and put in an ABB580. Will this motor run on a 580? I wonder if there is some priority wiring to look for?Sounds like maybe the pressure sensor is blocked or broken as when off should rear 0mh / 0 psi
Monday I will try again (since I can now get normal mode) to swap AI1 with AI2 and swap all control parameters to reflect new psi input. Also will try AI1 reading feet as in a tank level control. Change setpoint to a feet level. I‘ll update as time allows. After this if it doesn’t work, out comes the blue blade….Discharge pressure is in discharge line, reading outlet pressure continuously. It is the controlled parameter. This pump will run in manual at a set speed. but when switched to normal it just stops. We are beginning to think there is an issue with the electronics in the controller itself since nothing we can do will make it run in auto (normal) to control, pressure. Unless we are missing something, which is one reason I am here. Several Grundfos techs have looked at it to no avail. My next step is to rip the vfd and control out and put in an ABB580. Will this motor run on a 580? I wonder if there is some priority wiring to look for?
We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.