Grundfos MLE 132E speed control

View the thread, titled "Grundfos MLE 132E speed control" which is posted in Industrial Plumbing Advice Forum on UK Plumbers Forums.

We have a Grundfos for a domestic water booster application. Everything is set up for constant pressure, discharge pressure sensing and all appears okay, except we cant get the motor to run in "auto". We can run in manual at a constant speed, okay. But we try and go to control, the pump will stop. DI1 is set up as "stop". Now I've tried ground on DI1 as suggested, no change. 5V on DI1, still no change. We have discharge pressure reading, setpoint higher than pressure. Am I missing something simple?
 
Surely there's some software in the controller to stop the pump, ie if it sees no change in pump speed after a few minutes if in auto in constant pressure mode as you don't want the pump running constantly say at night with no demand?.
 
Surely there's some software in the controller to stop the pump, ie if it sees no change in pump speed after a few minutes if in auto in constant pressure mode as you don't want the pump running constantly say at night with no demand?.
Basically, we can not get a 'normal' operating mode selection, only stop, min, max. The start/stop terminals 2+3 (GND and DI1) are connected as per instructions for no external start/stop.
 
You will require the dongle to set up auto as the front line / bar graph is only for manual
 
Yes that’s the device use your phone and the grundfos go app
Update. We got the ir to work and it controls everything the front display does but like was stated it got the "normal" control mode to work, what happens is the pump normally shows stop, then when you push the start/stop button, the mode changes from stop to normal and you would expect the pump to start however it doesn't, it just sits there in normal mode.
 
So you can see all the settings on your phone etc and make changes / set things ?
 
Front display? That’s yours as that’s the 132e

1661512428170.png
 
I see on the pump you should be able to see a pressure when it’s running correct ?
 
Sounds like maybe the pressure sensor is blocked or broken as when off should rear 0mh / 0 psi
 
Sounds like maybe the pressure sensor is blocked or broken as when off should rear 0mh / 0 psi
Discharge pressure is in discharge line, reading outlet pressure continuously. It is the controlled parameter. This pump will run in manual at a set speed. but when switched to normal it just stops. We are beginning to think there is an issue with the electronics in the controller itself since nothing we can do will make it run in auto (normal) to control, pressure. Unless we are missing something, which is one reason I am here. Several Grundfos techs have looked at it to no avail. My next step is to rip the vfd and control out and put in an ABB580. Will this motor run on a 580? I wonder if there is some priority wiring to look for?
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Grundfos MLE 132E speed control" which is posted in Industrial Plumbing Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
Earmic,
Last reply from
Earmic,
Replies
25
Views
4,053
Back
Top