All very strange, the difference in pump heads should only increase the flowby ~ 15% so possibly blockage.
You replied to my post in that other site re reducing d.0 to ~ 7kw to get the boiler flow temp to fall, then increase it in 1kw steps until the flow temp returns to 70C, can then calculate the exact flow rate. Do this on CH only and on main pump red speed3. Close the manual bypass valve fully and then open it to its original setting of 1/2 turn open before starting.
 
Should have said shut the bypass fully and if the boiler keeps running then cary out the test above, ch only on, pump speed 3.
 
Sorry @John.g, I am confused on what you are asking me to do. Are you John Carroll on the other forum (buildhub.org.uk) where you replied to my post? If so, would you mind listing the steps you want me to do?

If you’re not John Carroll on the other forum, if you can outline again what you want me to do, that will be very helpful
 
OK, with CH only on, ensure main red pump on speed 3 (8M), when the boiler flow/return temps are steady and when the boiler flow reaches ~ 70C (its present setting), shut the manual bypass valve fully and if the boiler continues to run continuously again note the boiler flow/return temps. Then reduce d.0 to say 7kw, the boiler flow temp should then start falling, then steadily increase d.0 until the flow temp again reaches ~ 70C, note the flow/return temps, you now know what output (within reason) the boiler/CH system requires, we can then calculate the actual flow rate quite accurately from the above.

When test completed reopen the manual bypass valve a 1/2T again and again note the flow/return temps after another say 5 minutes.
 
Last edited:
Just a follow up question if someone can help.... if I have a system boiler installed with closed couple tees, do I still need an external pump(s)? I am aware that the existing UFH manifold pump is needed for the UFH system.
 
Yes for the ufh manifold the pump isn’t rated for the heating pipework from the boiler etc

So you will need two or theee depending if it’s a system boiler/ combi or heat only
 
Yes for the ufh manifold the pump isn’t rated for the heating pipework from the boiler etc

So you will need two or theee depending if it’s a system boiler/ combi or heat only
thanks @ShaunCorbs. Just to clarify, for a system boiler:
  1. internal pump contained within system boiler
  2. UFH manifold pump - pump already exists
  3. is another external pump(s) required for central heating?
 
point 2 the manifold pump isn’t rated to pull from the pipework so you will need another one here

Point 3 yes
thanks @ShaunCorbs.

Just to add some context, I am looking to replace my heat-only boiler with a system boiler. I already have an external pump beside each of my zone valves - photos attached of zone valves marked 1 = HW, 2 = UFH, 3 = CH

The external pump is a UPS2 25-80 (photo attached). Any issues with this pump being used for the central heating?

From what you have said, the manifold pump isn’t rated to pull from the pipework so you will need another one here. Can you expand upon where another pump will need to be fitted?
 

Attachments

  • Pump and valves marked.jpg
    Pump and valves marked.jpg
    507 KB · Views: 51
  • Main pump.jpg
    Main pump.jpg
    470.6 KB · Views: 47
One of the CCT (or LLH) advantages is that the primary circulating flow can be controlled to give a flow high enough to control the maximum dT which can exceed the boilers max allowable, generally ~ 25C, another advantage is that it helps to get the boiler away without exceeding the flow temp tripping point since all gas boilers fire up at ~ 65% of max output for up to 60 secs before modulation. The disadvantage is that the boiler return temperature increases with reduced demand.
For example if you set the primary flow to 14.3LPM to give a dT of 20C with a 20KW rad demand, the boiler dT will be 20C with flow/return temps of 65C/45C, a rad demand of 9kw will result in a dT of 9C, flow/returns of 65C/56C, a UFH demand of 9KW will result in the same dT of 9C with flow/return of 65C/56C. A rad demand of 2.5KW will give a dT of only (theoretically0 2.5C with flow/return of 65C/62.5C and the same for a UFH demand of 2.5KW.
Of course it will not prevent cycling if the minimum boiler output is greater than the heating demand.
 
Is a CCT/LLH required?.
The above boiler, a Vaillant 438, has a HEX with dP of 4.05M at a flow of 27.2LPM.
If a manual bypass was installed then opening it to give a 10.7LPM permanent by pass will result in a HEX dP of 3.5M (at 25LPM) which leaves 4.5M (8M UPS2 installed) remaining head to circulate 14.3LPM through the rads etc.
You will then end up with (boiler) flow/returns of rads only 65C/53.5C, dT 11.5C, UFH 9kw only of 65C/60C dT 5C, UFH 2.5KW 65C/63.5C, dT 2.5C..

If you could source a true constant curve pump then a ABV could be used to get much improved, lower boiler return temperature and greater boiler efficiency.
 
Last edited:
@ShaunCorbs - thanks for this.

From the diagram you provided, would:
  1. the 'heat source' be the equivalent of the new system boiler and the 'primary circulator be the internal pump within the system boiler?
  2. where it shows the "secondary circulator along with the 'spring loaded check valve' - would this be for the CH or UFH?
  3. and for the "another secondary circuit" - would this be for the UFH or CH?
  4. from the two secondary circulator pumps shown on your diagram, where would I use my existing 25-80 pump?
  5. similarly, where you mention about the need for an additional 15-5/60 pump for the UFH, where would this be located?
If you were able to provide a quick sketch of how my system should be set up, this will be greatly appreciated.

At the end of the day, what I am trying to achieve is to be able to run the UFH on its own without the boiler continually cycling. When this happens, the room that contains the UFH hardly heats up so the way I get around this is to run the CH at the same time so that the boiler continually runs and the UFH room heats up.

I had a look at the latest Vaillent ecotec plus system 25kW boilers which have a modulation range of 1:10 ecoTEC Plus - https://www.vaillant.co.uk/for-installers/products/ecotec-plus-610-615-620-625-630-635-154880.html. I was wondering if this would reduce the boiler cycling with just the UFH on?
 
That would be the rads as it’s the hottest heat load

Then the ufh eg horizontal one

25-80 for the rads

15-60 for the ufh

Same as drawing horizontal set

You want the highest modulation possible eg lowest kw figure of ideally under 1kw if possible

Only just seen you sent me a only sorry will have a look later
 
sorry @ShaunCorbs but I don't fully understand your reply based on the diagram you provided.

From your diagram:
  • where it shows the "secondary circuit & circulator along with the 'spring loaded check valve' - is this the CH circuit and the secondary circulator being my existing 25-80 pump?
  • where it shows the "another secondary circuit" - is this the UFH circuit, and where the pump is shown, is this the additional 15-5/60 pump you refer to, for the UFH?
 
many thanks @ShaunCorbs. On the Hydronic CCT, stupid question but what do the symbols (attached) denote? From your diagram last week, you showed the position of two CCTs, spring-loaded check valve and purging valve - where would these appear on the Hydronic CCT diagram?

On the System CCT diagram, I just see the 25-80 pump but do not see the 15-80 pump, nor the CCTs, check & purging valves - I they not needed?

Are there any advantages with the Hydronic CCT setup over the System CCT setup, and vice-versa?

1695885589029.png
 

Official Sponsors of Plumbers Talk

Similar plumbing topics

D
Replies
6
Views
2K
Boiler Advice Forum
Deleted member 126459
D
A
Replies
2
Views
1K
Boiler Advice Forum
Deleted member 120897
D

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.