40/30 is the ideal layout for UFH. (But good for heat pumps too.) If you then want to integrate radiators without a high temperature circuit that is the way to size the rads. Or if you are struggling to get enough output from your floor area you can top up the remaining heat output via suitable calculated radiators.Uponor only give MLCP friction tables for 82/71 and 70/50deg.
Agree that the boiler specs refer to 20deg drop, I have numbers for 80/60 and 50/30. That said, Junkers Bosch have one solar boiler with 40/30 in Germany/ Spain.
55/45 is the radiator calculation based on over in Germany for example.
Every better radiator manufacturer has spread sheets based on these temperatures. Trying to balance a system to 60/40 means strangling the radiators quite heavily with a possible "cow tail" effect on the heating once you have a certain amount of TRVs closed already.
As for the Uponor high temperatures I would not advise using MLCP pipe of any manufacturer at those temperatures. That is possibly the only downside of MLCP pipes that vapor could diffund (right wording?) at high temperatures between the PEX layer and metal layer and form blisters and possibly delaminate the layers. That is how they limit normal use temperature to 70 degC. Short term peaks are no problem at all. They say not to exceed 100h but they do not state over what period.