Please don't forget that your system still has to be compliant with Part L of the Building Reg's ? (an auto one is a requirement, if a by-pass is required) Leaving a rad without a TRV fitted is only allowed for the room with the room thermostat installed (it is providing the "boiler interlock") & this is to stop conflict between them not so it can maintain a min flow rate in the system.
There is 180m2 of space but all on one level and 2 of the 3 bedrooms have daytime use- the 'true' bedroom has only 1 rad with the TRV set at 16deg. Its hard to justify the cost/ time for an additional circuit for one radiator (8% of total requirement)
Yes, control rad will be near thermo and we there will be an external sensor too.
So, back solutions to run at 50/30 (or 60/40 or 70/50). So I could add an ABV and restrict less the flow across the control rad and the 3 towel holders. Anything else to reduce cowtailing/ cycling?