Interested to know where you guys take you fused spurs from and how do you size the cable/fuse at the board to it?
 
If there is a ring main close by I would take the spur from the ring main, the cable should be the same size as the ring main I.e. 2.5 mm t&e, the ring main protective device would suffice, and then the spur should be fused to protect the appliance as required.
Should I have to go back to the board for a new circuit then again 2.5 mm t&e, protective device for this would be 16amp then again fused at the spur to protect the appliance.
 
Last edited:
If there is a ring main close by I would take the spur from the ring main, the cable should be the same size as the ring main I.e. 2.5 mm t&e, the ring main protective device would suffice, and then the spur should be fused to protect the appliance as required.
Should I have to go back to the board for a new circuit then again 2.5 mm t&e, protective device for this would be 16amp then again fused at the spur to protect the appliance.

it might not be 16amp maybe 32 amp depends on what type of main they have used
 
If you read the text you will see that the 16 amp is to protect 2.5mm t&e, 32amp is to big to protect 2.5mm as a single circuit.
 
That was why I asked the question. 2.5mm from the board on a 15amp 3036 rewireable fuse to the immersion. Then a 1.5mm from the spur to the boiler with a 3 amp fuse at the spur. Just thought the 15amp at the board should be changed to a 6amp. Wasn't sure with the 2.5mm t+e.
 
Last edited:
He's not converting a radial into a ring he was asking where we take a spur from, and how we size the cable,
 
That was why I asked the question. 2.5mm from the board on a 15amp 3036 rewireable fuse to the immersion. Then a 1.5mm from the spur to the boiler with a 3 amp fuse at the spur. Just thought the 15amp at the board should be changed to a 6amp.

quick question does it need rcd protection and whats the bonding like 4mm on water 😉
 
He's not converting a radial into a ring he was asking where we take a spur from, and how we size the cable,

no but you need to know what your spuring from else you might overload a circuit

and that link was for you as you said 32 amp was too big for 2.5mm
 
As a single circuit, I.e. From the board to the appliance (not a ring main) then the maximum current carrying capacity of 2.5 mm t&e is 27amps when ref.method C is used, a 32amp breaker would therefore be too big.
 
As a single circuit, I.e. From the board to the appliance (not a ring main) then the maximum current carrying capacity of 2.5 mm t&e is 27amps when ref.method C is used, a 32amp breaker would therefore be too big.

yes but he didnt say what type it was and you suggested it was a ring post 5 and my post refers to yours
 
Good example of how a simple question can involve complex considerations. Next someone will ask is the cable surface mounted or surrounded by rockwool.
 
Cables are often oversized. I never use any heavier cable to a boiler than 1.0mm and that is more than plenty.
Fuses are for protecting cable to appliance and, perhaps slightly less importantly, the appliance itself.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "fused spurs" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
stratplus,
Last reply from
stratplus,
Replies
120
Views
3,094
Back
Top