Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

View the thread, titled "fused spurs" which is posted in UK Plumbers Forums on UK Plumbers Forums.

You can spur, and extend from a radial circuit as long as the cable is sized correctly. Its not great practice to spur from an immersion heater radial though as the OSG appendix 8 says that water heaters of 15l capacity or more should be on there own circuit.
 
You can't spur off a radial circuit!

Just for the record I never wire boilers hense all the questions/confusion!
Croppie are you saying that you cant change an immersion for a fcu?? Thought this was standard on refurbs to use the old immersion for the new boiler?
 
You can spur, and extend from a radial circuit as long as the cable is sized correctly. Its not great practice to spur from an immersion heater radial though as the OSG appendix 8 says that water heaters of 15l capacity or more should be on there own circuit.

The osg says about spurring off ring mains, one spur per outlet (or double outlet)

Categorically states not off radials.
 
Just for the record I never wire boilers hense all the questions/confusion!
Croppie are you saying that you cant change an immersion for a fcu?? Thought this was standard on refurbs to use the old immersion for the new boiler?

you can when you remove the immersion/cyclinder but you can spur off an immersion circuit with the immersion still in use
 
Flex is used because of the fact the front control panel is made to move for access, flat t&e is used for fixed wiring, and I can't remember pyro being used for anything that could move.
So what if the boiler cable is totally seperate/nothing to do with the fold down panel?!
 
Just for the record I never wire boilers hense all the questions/confusion!
Croppie are you saying that you cant change an immersion for a fcu?? Thought this was standard on refurbs to use the old immersion for the new boiler?

Course you can do that, senseless not to. But you'd be changing the immersion isolator to a FSS to feed the wiring centre. Any remote isolators, such as in the kitchen, for example, would need to be turned into a junction and blanked off.
 
Course you can do that, senseless not to. But you'd be changing the immersion isolator to a FSS to feed the wiring centre. Any remote isolators, such as in the kitchen, for example, would need to be turned into a junction and blanked off.

This example is just for a combi. so cylinder gone, immersion switch changed to fcu for combi.
 
The osg says about spurring off ring mains, one spur per outlet (or double outlet)

Categorically states not off radials.

Have to disagree there, although not got an OSG to hand to check. Spurring from radial circuits
when fused and wired correct is no issue at all. A 16A radial circuit run in 2.5mm T&E for instance cannot result in overloaded cable if the spurred cables are in 2.5mm T&E.
 
Have to disagree there, although not got an OSG to hand to check. Spurring from radial circuits
when fused and wired correct is no issue at all. A 16A radial circuit run in 2.5mm T&E for instance cannot result in overloaded cable if the spurred cables are in 2.5mm T&E.

I can't agree withyou. No point in both of us being wrong.

Especially as I happen to be doing my part P this week.

Your move batman.
 
no fcu should be by the boiler as to isolate the boiler and not having to search half the house to find it

Ok, so if you were to utilise the old immersion circuit and change the faceplate to a fcu, would you run another cable to a second fcu by the boiler? Never taken any notice before now tbh.
 
Ok, so if you were to utilise the old immersion circuit and change the faceplate to a fcu, would you run another cable to a second fcu by the boiler? Never taken any notice before now tbh.

the boiler going in the airing cupboard?
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "fused spurs" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

stratplus

Plumber
Gas Engineer
Plumbers Arms member
Joined

Thread Information