Ok but on the evening 8pm it was reading 3.5bar nothing using water and in the morning 5am it was 1.5bar nothing using water and as the gauge is after reducing valve I thought it should always show the set pressure not fluctuating supply?no all that is happening is that at different times of the day there is differing demand on the mains i.e. over night there will be less demand so pressure rises and during the day there is more demand so pressure will be lower.
you need to take the reading on the gauge while you have a tap running and set it as a working pressure.
it sounds like the main has a fluctuating pressure and has probably had an increase in pressure from work or being turned up by the supplier which is not uncommon when demands increase and decrease. this is more common in industrial areas.
I'll give that a go.
I still don't understand how if I set the pressure on the gauge which is on the outlet side of the valve at 2bar any fluctuation on the inlet pressure, increases the gauge reading as it has to pass through the PRV which is set to 2bar. This would suggest it's not working or am I get things confused?