H
Heating-eng
All pipework for gas needs this, most boilers need at least 22mm even some of the heat only boilers need 22mmNo, 1mb between meter and boiler, 1.5 mb between boiler and test nipple
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
All pipework for gas needs this, most boilers need at least 22mm even some of the heat only boilers need 22mmNo, 1mb between meter and boiler, 1.5 mb between boiler and test nipple
no they don't, they say no smaller than the boiler connection, some will work on a small amount of 15mm. Not combisWB says no less than 22mm at any point in the gas run
WB says no less than 22mm at any point in the gas run
even 22mm is too small sometimes, been to quite a lot on 22 with undersized gas.Depends what boiler, RIs can have 15mm now
i agree in part but it does matter what the manufactures say, worcester did say 22mm for a 12kw boiler and you had to comply ,now they say 15mm is ok,i dont really get this use of the statement's "this manufacturer said this" and "this manufacturer said that".
it does not really matter what they suggest, a 15kw worcester or 15kw baxi or a 15kw whatever, no change in what is required. what matter's is you design/size the pipework correctly.
Most of what manufacturers state in there instructions is used by engineers as an excuse from my experience. If your using manufacturers instructions to help you decide or excuse what size gas supply you fit then you need to reevaluate your methods imo.
Not when commissioning the boiler, I think they say upto 2.5mb drop on an existing boiler (service) but that's just going on memory.Dont WB let you have a 2.5mb drop between meter and boiler?
i agree in part but it does matter what the manufactures say, worcester did say 22mm for a 12kw boiler and you had to comply ,now they say 15mm is ok,
You still need to size the house correctly.
Hi All,
Just trying to get some clarification on the 15 or 22mm gas connection. I have a colleague who insists on getting all his installs changed to 22mm. I have also had confirmation from clients that BG insist on this as well but I was working under the rule of pipe run with bends and other gas appliances at max being under 1mb drop from meter to boiler?
Most boilers appear to have 22mm connections but I am fitting a Glowworm flexicom this week that has 15mm gas connection, so do you always follow manufacturers instructions but hat applies when not mentioned in the MIs?
Thanks
Kewat66