Don't think so although I'll have another good read tomorrow. I've kept an eye out for flow restrictors but not filters so will have a good check. ThanksAny mention of a flow restrictor or filter in the boiler mnual?
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Don't think so although I'll have another good read tomorrow. I've kept an eye out for flow restrictors but not filters so will have a good check. ThanksAny mention of a flow restrictor or filter in the boiler mnual?
I'll try and do this. Think there is a point where the mains enters the property where I could attach a gauge and take a reading. Not sure about after the boiler though in terms of attaching to taps etc but will look into it. ThanksNo, the boiler pressure has nothing to do with the problem.
The pressure drop through 40 ft of 22mm piping even at a flow rate of 20 LPM is only ~ 0.15 bar, as someone pointed out the problem may be on the hot water outlet to the users, you or somebody will have to take pressure readings before/after the boiler to narrow down the problem.
I'll check for that in my manual tomorrow and ask the fitter to reclean the filter assuming the flow restrictors can't be cha he'd or removed. Much appreciatedYes, there is a restrictor and a filter.******.
Navien NCB-180 Installation & Operation Manual (Page 22 of 77) | ManualsLib
www.manualslib.com
Had a quick look at the manual I have here and there's no mention of flow restrictors just something about cleaning the return adaptor filter on page 51 which I assume isn't it? I've attached the manual it would be great if you had a sec to see if there's anything obvious that could have been missed. I'm going to try at some point today to measure the mains pressure just after the stopcock just so I can be sure what pressure is coming in. ThanksI would think, if installed, that they can certainly be removed.
It shows a differential pressure of ~ 2 bar is required for a flow rate of 20 LPM so would probably need 3 bar mains pressure to give 1 bar at the boiler inlet,
at 12 lpm the deltaP required is ~ 0.9 bar so the mains pressure would be ~ 2 bar at this flowrate to give 1 bar at the boiler inlet., these restrictors, if fitted, can have a very significant effect on the final flowrate IMO.
I will clarify the page 23 with the installer so thanks. I've just attached the PG to the point just after the stopcock....today around 15 mins ago it measured 2.2bar. Assuming it must fluctuate if I got 3 bar previously an outside tap. (The outside tap was the same 2.2bar btw) cranked up the boiler temp to maximum 65 degrees and opened a few outlets. The PG changed to 2bar lowest...it didn't move much at all. I'm not sure what this means I'll be honest, I just can't figure a way of measuring the pressure beyond the boiler although hopefully my fitter will have something for this. If I felt confident at removing the filling loop I'd try and measure the flow rate before it hits the boiler.I don't see any reference to cold water restrictors but on page 23 it states "After installing the boiler clean the cold water inlet filter", this of course may only refer to a typical installation but it is mentioned.
Re monitoring pressure, you have a 3 bar PG at the outside tap so when no flow through it but with flow through the combi should tell you something as it should reflect any pressure drop at the mains, just switch in the DHW and watch it, you really want another PG somewhere at the end of hot water supply to the house. Also even though it shouldn't have any effect on the flow through the boiler turn up the DHW temp control knob to max while doing the tests.
What was the kw output of your old Istor? did flow rate feel ok?
Was hoping to reply this eve with some info from Navien as I was contacted today by the boiler fitting company saying the installer had spoken to Navien earlier today. No phonecall as yet so I can't really update.That was from two taps.***. "Just opened two hot taps - one in a sink next to the boiler and one in a sink upstairs in the kitchen (boiler in basement). kitchen was 5.4lpm and basement tap 7.2lpm" so kitchen was 5.4 LPM.
Would like to know the deltaP through its plate Hx or through any combi for that matter.
The old boiler, not sure if a combi but with a HW cylinder as well was giving much better flow rates through the showers and HW taps and it was the same cold water line supply so the only big change is the boiler itself?.
The gas supply has nothing to do with the flow rate, you could have the boiler switched off and it won't affect the flow rate. A 20kw combi can give the same flowrate as a 40kw, it just wont be as hot.Was hoping to reply this eve with some info from Navien as I was contacted today by the boiler fitting company saying the installer had spoken to Navien earlier today. No phonecall as yet so I can't really update.
Yes previously the ideal istor was an all in one unit of a 24kw system boiler (an icos or something similar) attached to an unvented cylinder. It had a prv at the mains set to 2bar which has since been replaced with a straight pipe and the flow from taps was far superior. I never did take any measurement but a bath would fill up in no time....now I'm sitting around for a while longer. Cold tap is no different than previously so no issues with the cold supply.
All the same pipework other than the 22mm pipe serving the boiler has been reduced to 15mm where it connects and the prv removed so pressure now makes its way up to 3bar. I've attached a pic...assuming it all looks ok?
The gas supply crossed my mind just simply with it being a bigger KW boiler but probably thinking on a bit of a simplistic level for that justification.
Thanks
I'm going to ask the fitter to do this for me as I'm a bit uncertain how to go about it. Funnily enough I did ask him to do this during the installation before connecting up the boiler but he didn't have a flow cup on the van!Have you tested the lpm at the boiler yet ?
I'm going to ask the fitter to do this for me as I'm a bit uncertain how to go about it. Funnily enough I did ask him to do this during the installation before connecting up the boiler but he didn't have a flow cup on the van!
Just followed your instructions nice and straightforward thanks. Although the boiler has a dedicated feed in 22mm pipe using that method I get spot on 9lpm....which corresponds nicely with the boiler readouts.5l bucket or 1l bottle work well just time hoe long it takes to fill either and work it out how many you can fill in 60 seconds
for example if a 1l bottle takes 10 seconds to fill your running 6lpm etc if it takes 5 seconds it’s 12lm etc
you can do this via the filling loop will give an approximate gauge
eg turn the black lever off turn the blue lever off
disconnect the flex from the black lever side on the silver nut
put this into a 5l bucket or aim get your timer ready when ready open the blue lever fully and start timer etc
Just followed your instructions nice and straightforward thanks. Although the boiler has a dedicated feed in 22mm pipe using that method I get spot on 9lpm....which corresponds nicely with the boiler readouts.
I gather this is why I'm not getting the desired flow rates?