A question related to CO2 FGA failing on minimum rate.
View the thread, titled "A question related to CO2 FGA failing on minimum rate." which is posted in Gas Engineers Forum on UK Plumbers Forums.
I am going back to a Worcester Greenstar 30 CDi Classic that's failing a CO2 emissions test on minimum rate only. I do adjust the gas valve but there is zero effect. I haven't mixed up the "min" and "max" adjustment screws.
What could be causing this boiler to fail on minimum only? It's perfect at max rate, heat exchanger is clean (fan pressure test) and everything else is OK.
Which did you adjust for high ?
Tbh would clean and fully service the boiler first before making any adjustments
Nothing, I put the adjustment key in to adjust what I thought was the low. 1/4 turn, no change. 1/4x2 more. No change, so turned it back to where it was and started looking at the boiler baffled. Maximum rate was OK. I thought the little 2.5mm screw just above the the adjustment screw on the valve was the minimum rate ffs. I'll do this tomorrow. Lesson learned. READ the manual regardless. The application for air/gas ratio is different on this, it's the first time I've encountered this.
Centre behind the Allen bolt is low it’s touchy so 1/16 at a time and let it settle over a few mins for adjust it another 16th
sorted , perfect readings. Yes, the 1/16th turns is actually still crazy heavy on the adjustment believe it or not!!! But when you adjust the max you have to adjust the min and likewise. It was just very sensitive to the adjustments. That's the first air/gas ratio I've had to call the manufacturer.
Reply to the thread, titled "A question related to CO2 FGA failing on minimum rate." which is posted in Gas Engineers Forum on Plumbers Forums.
DTBoilerDude,
DTBoilerDude,
