L
LPC
Went to a no heating/hot water today on a Vaillant Turbomax 242. As soon as I unscrewed the first screw holding the combustion chamber on, water started ****ing out from the seal. Got a good quarter bucket of water out of it before I could get the cover off. Pressure was fine so heat ex couldn't be perforated. The inside looked like this:
http://i.*********/2uxQQiJ.jpg
So i'm pretty puzzled at this point. Couldn't see a leak or anything. Then I spot it; the PRV going through the flue hole, directly next to the flue. I've seen quite a few PRVs going up before so didn't think much of it before, until I saw this.
http://i.*********/yQ0NUxs.jpg
So I went out of the flat and round to have a look at the flue. It's 3 storeys up so I couldn't get a picture today but i'll try and get one when I go back, but this drawing shows exactly what is there:
http://i.*********/eCGLaFQ.jpg
The PRV runs directly alongside, and terminates outside directly next to the air intake of the flue. The prv had obviously discharged and the boiler had sucked the whole lot into the combustion chamber. The end of the PRV pipe is exactly as this shows, right next the air intake holes, and even closer than this drawing shows.
ID'd is obviously and going back Wednesday to move the PRV under the boiler and clean it up a bit. All this because the installer was too lazy to drill a 15mm hole.
Funnily enough this passed a landlords safety inspection 4 days ago (not me obviously) 🙂
http://i.*********/2uxQQiJ.jpg
So i'm pretty puzzled at this point. Couldn't see a leak or anything. Then I spot it; the PRV going through the flue hole, directly next to the flue. I've seen quite a few PRVs going up before so didn't think much of it before, until I saw this.
http://i.*********/yQ0NUxs.jpg
So I went out of the flat and round to have a look at the flue. It's 3 storeys up so I couldn't get a picture today but i'll try and get one when I go back, but this drawing shows exactly what is there:
http://i.*********/eCGLaFQ.jpg
The PRV runs directly alongside, and terminates outside directly next to the air intake of the flue. The prv had obviously discharged and the boiler had sucked the whole lot into the combustion chamber. The end of the PRV pipe is exactly as this shows, right next the air intake holes, and even closer than this drawing shows.
ID'd is obviously and going back Wednesday to move the PRV under the boiler and clean it up a bit. All this because the installer was too lazy to drill a 15mm hole.
Funnily enough this passed a landlords safety inspection 4 days ago (not me obviously) 🙂