Called to move some pipes. One is gas. 30m 28mm. Ecotec 656 boiler. Obviously undersized. Ran checks to see how was performing. 17mb at boiler with hob on. Just in tolerances of vaillant mis. Only 17mb however as standing 28mbar.
Gas rate erratic as boiler modulating i think even on low loss header with call for heat and p1. I say this as i got four different results. The last being 65kw.
Vaillant technical said they only allow 4 mb drop from standing to working at boiler.
At risked and said she should get them back to redo. Only did it last year and obviously couldnt be bothered with the expense of running new gas.
Prv returned to the condense below a hep non return. No tundish
Gonna ring them today to talk it through.
Shes emailed the at risk form so theyve got all my details which is a shame as i didnt get anything from the situation.
Gas rate erratic as boiler modulating i think even on low loss header with call for heat and p1. I say this as i got four different results. The last being 65kw.
Vaillant technical said they only allow 4 mb drop from standing to working at boiler.
At risked and said she should get them back to redo. Only did it last year and obviously couldnt be bothered with the expense of running new gas.
Prv returned to the condense below a hep non return. No tundish
Gonna ring them today to talk it through.
Shes emailed the at risk form so theyve got all my details which is a shame as i didnt get anything from the situation.