I can't help wondering if the system has been balanced for the correct temperature differential.
The British Gas 330 boiler has a maximum output of 30kW but is set, at the factory, to give 18kW. As there are only 13.5kW of rads, I would assume the output has not been changed. The boiler is designed to have a flow-return differential of about 20°C. With a 20°C drop the head loss through the boiler, at 18kW, is about 0.9m. This would leave about 3m available from the 15-50 on speed 3 for the head loss in the radiator circuit.
If the system has been balanced for a differential of about 10°C, the flow rate will double and the boiler head loss alone will be about 3.6m (four times greater), which is more than a 15-50 can deliver. This would not someone trying to balance for an 10°C, even if they could only achieve something higher.
The British Gas 330 boiler has a maximum output of 30kW but is set, at the factory, to give 18kW. As there are only 13.5kW of rads, I would assume the output has not been changed. The boiler is designed to have a flow-return differential of about 20°C. With a 20°C drop the head loss through the boiler, at 18kW, is about 0.9m. This would leave about 3m available from the 15-50 on speed 3 for the head loss in the radiator circuit.
If the system has been balanced for a differential of about 10°C, the flow rate will double and the boiler head loss alone will be about 3.6m (four times greater), which is more than a 15-50 can deliver. This would not someone trying to balance for an 10°C, even if they could only achieve something higher.