Baxi combi instant 80 he , no hot water
View the thread, titled "Baxi combi instant 80 he , no hot water" which is posted in Bathroom Advice on UK Plumbers Forums.
flesi
Working on Baxi combi instant 80 he, it works on heating but not hot water. New diverter valve and new plate heat exchanger installed by another engineer still no hot water. Can anyone shed any light?
Hot water flow switch sticking or diaphragm split perhaps or the microswitch faulty? Have you checked to see if the switch is being made and if so you need to check for continuity through the switch .. 1st thoughts... 🙂
Any lights flashing? Does it fire up then go cold, burner off? If so then still looking at water flow switch. If a diaphragm is pinholed it can work briefly until the pressures equalize through the hole!
does the hot water demand light come on and stay on when a hot tap is opened? Turn the hot water control pre-heat stat to off when you test the hot water... see what happens 🙂 If the switch is making then that light should stay on perminent not flashing 🙂
I've got to go flesi ... sounds like you've proven that a demand for hot water is definitely being made.... so when there's no burner lit is the pump and fan running? If not check for continuity through the pump flow switch and aps? Without seeing what's happening it's hard to be exact mate .... Good luck and I'll catch up later see how you're getting on 🙂
as steve said either small dhw diaphragm split or valve snapped or ntc fault
Cheers gas man, the issue in the first place was no heating but hot water was ok. So the previous engineer has changed the diverter valve then heating was ok but not hot water. I did change the small dhw diaphragm still no hot water. I'll try the ntc tomorrow and see what happens but still I'm not convinced .
If u short out two green wires on microswitch does demand stay on ? If demand is constant sensor issue. Did pcb get a wash at all?
I washed one once by mistake - covered the control with a cloth and a bin liner over that and taped up and it still got wet water run down the wires into the board - didn't notice and turned it on that cost me
flesi, If the demand light's staying on and no burner then you got to know whether the pump is running and being proven, fan is on and being proven, if they're ok then you got to check out the hot water thermister, swapping its probably the easiest to do 🙂
Are you getting a flow through the plate hex? Does the boiler 'dump down' the heating flow?
Is the diverter actuator working?
You can put the boiler into heating mode, turn off preheat and demand heating, take the actuator off and manually move the spindle to see of the water flow is being diverted .. watch the burner/feel the heating flow and return to main hex above pump to see if you're getting a flow through the phex .. 🙂
steve do you know if the voltages on the diverter stay or not - went to baxi last wk on duotec hea and they said when call for htg diverter head powers for 15 sec to htg position then locks in and looses 240v when hw trhen the same powers to hw for 15 sec then locks in that position then 240v goes is it the same with the 105
Demand for hot water stays on and the burner comes on for few secs , pump & fan run, getting flow through plate hex. Pulled out the diverter actuator , u can see the pin moving when is heating demand. I'll check the thermistor tomorrow . Thx for your help.
Washed loads of them normally when doing diaphragm and the expansion is full of water and air lock moves! I just dab it dry and 3 mins with a hair dryer works a treat!!
For future reference, the block behind the DHW pressure differential valve blocked, pin was stuck in.
Stuck in pre-heat position yeh? - Never had that before but the symptoms make sense now 🙂 Cheers 'flesi'! If you check out the mi's there's a good schematic of how the valve works on pre-heat!
Always learning 🙂 :rockon2:
that is the hw priority valve . diverts to plate or pre heat bypass
You're right mate 🙂 Sounds like the op's got stuck in the bypass position. Boiler comes on full rate and quickly drops off as the flow is reduced through the bypass in the mean time the phex gets no/little flow through it 🙂 Symptom as op states ... Interesting eh? 🙂
that could have easily been mistaken for plate on diagnosis . hw water issues like that are the ones I struggle on as sometimes they are not the obvious
Yeh agree mate... I guess that's where touchy feely takes over 🙂 However Baxi are the only manufactures I'm aware of to take up this strange way of 'pre-heat' .... ! Most others pre-heat the phex and not a 'storage' in the expansion!! You'll always be caught out mate!
I've most likely mentioned it before but as an apprentice and ever since I've been taught and learned how most component parts work individually and work in with how the appliance itself functions ... ! I don't know how folk are taught these days but for me it's been an asset..!
Reply to the thread, titled "Baxi combi instant 80 he , no hot water" which is posted in Bathroom Advice on Plumbers Forums.
flesi,