Cheers gas man, the issue in the first place was no heating but hot water was ok. So the previous engineer has changed the diverter valve then heating was ok but not hot water. I did change the small dhw diaphragm still no hot water. I'll try the ntc tomorrow and see what happens but still I'm not convinced .as steve said either small dhw diaphragm split or valve snapped or ntc fault
link out the micro switch to eliminate that
I washed one once by mistake - covered the control with a cloth and a bin liner over that and taped up and it still got wet water run down the wires into the board - didn't notice and turned it on that cost meIf u short out two green wires on microswitch does demand stay on ? If demand is constant sensor issue. Did pcb get a wash at all?
steve do you know if the voltages on the diverter stay or not - went to baxi last wk on duotec hea and they said when call for htg diverter head powers for 15 sec to htg position then locks in and looses 240v when hw trhen the same powers to hw for 15 sec then locks in that position then 240v goes is it the same with the 105flesi, If the demand light's staying on and no burner then you got to know whether the pump is running and being proven, fan is on and being proven, if they're ok then you got to check out the hot water thermister, swapping its probably the easiest to do 🙂
Are you getting a flow through the plate hex? Does the boiler 'dump down' the heating flow?
Is the diverter actuator working?
You can put the boiler into heating mode, turn off preheat and demand heating, take the actuator off and manually move the spindle to see of the water flow is being diverted .. watch the burner/feel the heating flow and return to main hex above pump to see if you're getting a flow through the phex .. 🙂
Demand for hot water stays on and the burner comes on for few secs , pump & fan run, getting flow through plate hex. Pulled out the diverter actuator , u can see the pin moving when is heating demand. I'll check the thermistor tomorrow . Thx for your help.flesi, If the demand light's staying on and no burner then you got to know whether the pump is running and being proven, fan is on and being proven, if they're ok then you got to check out the hot water thermister, swapping its probably the easiest to do 🙂
i always remove the pcb Honeywell dry out nicely and survive Siemens dont the instants used bothWashed loads of them normally when doing diaphragm and the expansion is full of water and air lock moves! I just dab it dry and 3 mins with a hair dryer works a treat!!
Once followed a guy who'd replaced the PCB and got the knob spindles in wrong .. hot water was a bit dodge then too 🙂
For future reference, the block behind the DHW pressure differential valve blocked, pin was stuck in.
If u look on mi it's on page 37, fig.65 it's the block behind that valve.the hw priority valve ?
that is the hw priority valve . diverts to plate or pre heat bypass
that could have easily been mistaken for plate on diagnosis . hw water issues like that are the ones I struggle on as sometimes they are not the obviousYou're right mate 🙂 Sounds like the op's got stuck in the bypass position. Boiler comes on full rate and quickly drops off as the flow is reduced through the bypass in the mean time the phex gets no/little flow through it 🙂 Symptom as op states ... Interesting eh? 🙂
one of the possibilities i gave in post 10 hope you did not get ripped for it there keenly priced with abkotFor future reference, the block behind the DHW pressure differential valve blocked, pin was stuck in.
Reply to the thread, titled "Baxi combi instant 80 he , no hot water" which is posted in Bathroom Advice on Plumbers Forums.